Hello Plumbers and thank you Terry for having this awesome platform. I hope everyone is doing good and in good health!

Question, is it ok to install a T&P valve off this tee


messages_0 (3) TPR b.jpg
?

Yw2s86VzksnNSNSNA
 

Breplum

Licensed plumbing contractor
Messages
1,904
Reaction score
767
Points
113
Location
San Francisco Bay Area
1. T&Ps are not installed on tankless water heaters. What are installed is a pressure relief valve.
2. You need to have a bypass union kit at the tankless unit to allow for descaling on an interval appropriate to water conditions present. The bypass kit comes with a relief valve.
 

Holeshot

New Member
Messages
16
Reaction score
1
Points
3
Location
California
IMG_20200123_130306.jpg



Thank you! I see, it's a pressure relief valve, no need for the temp.

Yes, I'm installing isolation valves. There's a pressure relief valve installed at the tee.

Question
Is it ok to install isolation valves without a pressure relief valve attached directly to the isolation valve? Since there's already a pressure relief valve installed off the tee.

The photo above. This is a typical installation with isolation valves. Usually a pressure relief valve is attached directly to the isolation valve.
TLoxubuNNRoJbnWg9
 
Last edited:

Tuttles Revenge

In the Trades
Messages
4,132
Reaction score
1,410
Points
113
I think the port for the relief valve is between the isolation valve and the water heater so that its always there to protect in case the water heater fails while isolated or in the open position.
 

Holeshot

New Member
Messages
16
Reaction score
1
Points
3
Location
California
Thank you. I'll install some isolation valves. I'd like to screw the connector hoses directly to the isolation valves and cap off the pressure relief valve port.

There's an existing pressure relief valve that's installed off the copper tee.

Or do I have to hard pipe it to the isolation valves with the pressure relief valve?
 