I have been searching high and low for the answer, even called the support line for the insulation I plan on using. I live in NY and remodeling a small 20' x 8' room that is above a vented crawl space. I plan on using Roxul insulation between the joists that does not have a vapor barrier. Roxul recommends plastic as a vpaor barrier for my area. The sub floor is all new plywood. I would like to glue and use ring shank nails to fasten the plywood directly to the joists, however, if I use a plastic vapor barrier over the top of the joists (under the plywood), the glue will not be effective as I will be essentially gluing the plywood to the top of the plastic.
Any recommendations on what I should to are appreciated. Thank you in advance!
-Paul
IRC code min for floors over vented crawls or pier foundations in your US climate zone 4A location is R19, but R19 batts compressed to 5.5" in a 2x6 bay only performs at R19, and is barely more than an air-filter for resistance to air infiltration currents. A rock wool batt designed for 2x6 framing is R23 and FAR more air retardent, so you're thinking along the right lines.
First be sure to caulk all the seams of the band joist & foundation sill with polyurethane caulk. Use can-foam for any gaps bigger than 3/8" or so. Air leaking into or by the cavity insulation undercuts it's performance. And a square inch of air leaks moves far more moisture than vapor-diffusion through 1000 square feet of 3/4" plywood subfloor.
The only time moisture accumulation in the subfloor would be a problem in your area during the cooling season, when humid summertime air with an average dew point north of 65F enters the crawlspace (which is much of the summer.) In the winter the air in the crawl space has a dew point much lower than the temperature of the (warmer, insulated) subfloor, which will tend to dry it out. A couple of alternatives:
A> If you paint the bottom side of the subfloor with "vapor barrier latex" it will reduce both the drying & moisture accumulation rates of the subfloor. If the crawl space has ground vapor retarder to limit the ground moisture from entering the crawl space and the vents are open in winter it offers quite a bit of protection- the moisture content of the joists will rise and fall seasonally (which is potentially an issue for the joists), but the subfloor's moisture content will stay pretty stable. To prevent thermal bypass air currents, the rock wool needs to be snugged up to the subfloor, with no gaps. Having it snugged up like that keeps air from moving between the insulation & floor, but there will be some temperature striping on the floor over the joists detectable with bare feet during the coldest weather.
B> If you leave the subfloor unpainted and fill the joist bays completely (are they 2x6? 2x8? 2x10s? 2x12?) A layer of 1-2" foil faced polyiso cap-nailed to the bottom of the joists, seams taped with foil tape, and edges caulked to the foundation sill with polyurethane caulk (or can-foam) is more vapor retardent than 6 mil polyethylene, and will reduce the temperature striping issue completely. It takes at least 1" of polyiso to double the R-value of a 2x6, and 2" to double the R-value of a 2x12. More is always better, of course. Thinner polyiso can still deliver the moisture protection, but for the amount of effort it takes to hang sheet foam anything less than 1" hardly seems "worth it", and may not have sufficient R value to prevent condensation/frost at the foam/fiber boundary during winter.
If it were my house I'd be inclined toward B, unless it's simply impossible to get the sheets of foam in there. A 4' x 8' sheet of foil-faced goods can be scored at the mid-point with a utility knive and folded on the other facer into a 2' x 8' to fit through a 26" wide vent space, assuming there's sufficient room to unfold it there. Before the subfloor goes down it might be possible to slip them in from the top side in full 4' x 8' sheets, in which case it would be worth caulking them to the framing from the top side for enhanced air tightness, installing the batts from the top side prior to installing the subfloor.
What you DON'T want to do is to skip the foam or VB latex and staple a sheet of 6 mil poly on the underside of the joists. While that is protective of the subfloor in winter, it's all but guaranteed to be wet in winter when it's on the cold side of the assembly.
With a more detailed description of the floor assembly there may be other options that can work too.