Hi, I know the answer to this question but I’m really scratching my head and just wondering if I’ve forgotten something. I am feeding a subpanel on a dock from the main panel in my house. I have a 50 amp, 240 V breaker in the main panel. The supply from this breaker goes to a physical disconnect on the outside of the house. I have the breaker closed and the disconnect open. The disconnect only interrupts the two hot legs but not the neutral. From there, the feed goes to another disconnect switch at the dock before it gets to the subpanel. At that disconnect, both hot legs and neutral are interrupted. This switch is open.
Now, checking power at the first disconnect. I have 240 across the two hot legs. I have 120 from each of them to ground. Of course this also means I have 120 to the neutral, since neutral and ground are bonded in the main panel. Here’s the weird thing. I also have 120 from each of the supply side hot legs to the opposite leg on the load side.
Is there something obvious that I’m just brain dead about? I would not think I’d see any potential there.
Now, checking power at the first disconnect. I have 240 across the two hot legs. I have 120 from each of them to ground. Of course this also means I have 120 to the neutral, since neutral and ground are bonded in the main panel. Here’s the weird thing. I also have 120 from each of the supply side hot legs to the opposite leg on the load side.