Sta-Rite DS3HF-01 intermittently tripping breakers

Users who are viewing this thread

Scott Amendolaro

New Member
Messages
4
Reaction score
2
Points
3
Location
Florida
My Sprinkler pump recently started intermittently tripping breakers on startup. When it does start pump runs it is working fine .

I have noticed that the pump is buzzing pretty loud for sometime 5-10 seconds before the breaker trips. I looked at my TED monitor while this happened and it looks like the pump was drawing 10kw for 13+ seconds (@ 240) before the trip. When I reset and restart that delay is often about 4-5 seconds before it starts. So it definitely looks like the amp pull is causing it.

Not sure at this point if its the motor or the Cap and thought I would ask here what you thought before I went and bought a new motor.

The DS3HF is about 7 years old , running on an artisan well .

Thanks

Scott

(Below is a look at the Sprinkler pump turning on and when the breaker trips. Each dot is a second

breaker trip.jpg
 
Last edited:

Reach4

Well-Known Member
Messages
38,882
Reaction score
4,433
Points
113
Location
IL
I have noticed that the pump is buzzing pretty loud for sometime 5-10 seconds before the breaker trips. I looked at my TED monitor while this happened and it looks like the pump was drawing 10kw for 13+ seconds (@ 240) before the trip. When I reset and restart that delay is often about 4-5 seconds before it starts. So it definitely looks like the amp pull is causing it.

Not sure at this point if its the motor or the Cap and thought I would ask here what you thought before I went and bought a new motor.
Was the pump running during the high current draw? If no, replace the capacitor.
 

Scott Amendolaro

New Member
Messages
4
Reaction score
2
Points
3
Location
Florida
Was the pump running during the high current draw? If no, replace the capacitor.

No , when it runs the current draw is normal.

Thanks, I'll pick up a CAP .

It had a NGM 680171-007 189-227uf 110 in it . Couldn't find an OEM replacement so ordered a similar MARS2 11915 for $5.

I'll let you know how things go.
 

Scott Amendolaro

New Member
Messages
4
Reaction score
2
Points
3
Location
Florida
Usually burning a start cap means you are cycling the pump on/off too much. That start cap is only used during a start, so too many starts?


Depends what too many looks like , We are water restricted here ( since I've been here) so during the summer it only starts 4 times a week and during thee winter 2 times . The Relay actually went bad several weeks earlier but I could hear the long startup times long before that . I have had a near-lightning strike 2 years ago which damaged some equipment in the home , the pump wasn't one of them but it could have contributed
 