Alucard
New Member
Hello. This site is terrific. Anyway, the expansion tank I installed about 10 years ago sprung a leak so I needed to replace it. But, I saw that Sharkbite makes what they call a Thermal Expansion Relief Valve designed to reduce pressure from the expansion of water from the water heater, when pressure hits 125. The water just runs on the floor to the drain. It works okay. But, Sharkbite maintains that, if you have this valve, you don't need an expansion tank, so I purchased it and installed it. Now, without an expansion tank in our closed loop system, the water starts to heat up and expand, until it hits 125 or until someone turns on a faucet or shower. So, now, without the expansion tank, we get that initial high water pressure when someone turns on a faucet, just for fraction of a second. We do have a water pressure reducer about 10 feet from the water supply coming into the house, to reduce what comes from the street/water supply. But, this doesn't, nor is it supposed to reduce pressure from the water heater, as the water heats up. I have it set to about 70. It works as it should. I installed a water pressure meter to monitor this. Correct me if I'm wrong, and that happens often, but, with this sharkbite thermal expansion relief valve, pressure will build up into the system when the water heater does its thing until someone gets in the shower, or turns on a faucet or the pressure gets to 125. So, from the expansion of heated water, we will have anywhere from 70 psi to 125 psi, in our system without an expansion tank. So, we actually still do need an expansion tank. Is this correct?
Last edited: