Appreciate any help! We have a lake cottage with a very old F&W single line (suction) jet pump. Always drain the pump and household lines for the winter and have always been able to prime and go in the spring.
Not this year. The cold split the main supply line in the crawlspace, so we had to replace. Once we did, we can prime the pump and get it to build some pressure (24psi), but it keeps running on and on never coming close to the 40psi cutoff pressure.
When I open a faucet, we are just getting a lot of air and very little water. Left open for more than a few seconds the pressure falls out to zero and then I have to reprime the pump.
The well is outside the crawl and an iron pipe comes into the crawl. From there 1" PE pipe connects to galvanized with a check valve just before the suction port of the pump. I can feel cold water in the suction line about two feet below the check valve, but no cold water past the check valve at the suction or discharge side of the pump.
The gauge showing the slow build to 24psi when the pump is run is on the discharge side, between the pump and the tank. This pressure has held for at least 12 hours without dropping.
Leads me to believe the system is sealed from air leaks at least from the check valve through the pump and throughout household plumbing.
What are the possible culprits?
I'm leaning toward:
1) Possible issue with check valve not opening far enough to allow sufficient water to flow into suction part of the pump.
2) Clogged inlet/venturi of jet pump
3) Old jet pump simply not able to create enough suction to lift water all the way.
Are these reasonable assumptions or anything else to consider? How would you recommend proceeding?
Not this year. The cold split the main supply line in the crawlspace, so we had to replace. Once we did, we can prime the pump and get it to build some pressure (24psi), but it keeps running on and on never coming close to the 40psi cutoff pressure.
When I open a faucet, we are just getting a lot of air and very little water. Left open for more than a few seconds the pressure falls out to zero and then I have to reprime the pump.
The well is outside the crawl and an iron pipe comes into the crawl. From there 1" PE pipe connects to galvanized with a check valve just before the suction port of the pump. I can feel cold water in the suction line about two feet below the check valve, but no cold water past the check valve at the suction or discharge side of the pump.
The gauge showing the slow build to 24psi when the pump is run is on the discharge side, between the pump and the tank. This pressure has held for at least 12 hours without dropping.
Leads me to believe the system is sealed from air leaks at least from the check valve through the pump and throughout household plumbing.
What are the possible culprits?
I'm leaning toward:
1) Possible issue with check valve not opening far enough to allow sufficient water to flow into suction part of the pump.
2) Clogged inlet/venturi of jet pump
3) Old jet pump simply not able to create enough suction to lift water all the way.
Are these reasonable assumptions or anything else to consider? How would you recommend proceeding?