Called the inspection, but in the meantime was wondering if anyone sees any red flags. PEX is holding at 80 PSI, after finding some leaking threaded fittings with soap and water.

IMG_8994.JPG
IMG_8993.JPG
IMG_8992.JPG
IMG_8991.JPG
IMG_8990.JPG
IMG_8995.JPG
 

OLD TIMER

Member
Messages
181
Reaction score
14
Points
18
Location
FLORIDA
The toilet flange gets screwed down to the finish floor. To some it don't matter.
But it might to your inspector.
 
Last edited:

OLD TIMER

Member
Messages
181
Reaction score
14
Points
18
Location
FLORIDA
I forgot to tell you, you have to pressure test all those pipes and the inspector needs to see them under test. unless you already knew that.
 

Zane Bridgers

Member
Messages
77
Reaction score
4
Points
8
Location
Northern New Mexico - Climate Zone 5A
Thanks Old Timer! The slab is rough there around the penetration, but it will be stained concrete floors.

Good news is we passed the inspection! He said we could have run water lines in the wall and insulated, also maybe needed an offset toilet flange, and 2" VTR here because of the cold winters, so have to put a coupling before the 1.5" vent passes through the roof. We have to fill the shower pan with water for the final with a test ball.
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
The shower pan liner needs corner patches at the curb. Does it have a preslope underneath it?

Cheers, Wayne
 

Zane Bridgers

Member
Messages
77
Reaction score
4
Points
8
Location
Northern New Mexico - Climate Zone 5A
The shower pan liner needs corner patches at the curb. Does it have a preslope underneath it?

Cheers, Wayne

Yes, the pre-slope mud bed is under there, I haven't seen corner patches mentioned as a requirement elsewhere. Is this a nice to have or a must have? I folded the corners like a present so there are no cuts. Would the corner dams go in all corners or just the curb?

The shower pan liner also needs horizontal blocking between the studs (doesn't look like it has any). There's a nice article in the recent Fine Homebuilding magazine detailing code requirements for site-built shower pans; worth a look

Do you mean horizontal blocking just around the perimeter of the top of the liner? The inspector didn't say anything, but I guess that makes sense. I read the fine home building article - not sure there is anything I didn't come across previously, but a nice refresh.
 
Last edited by a moderator: