Hello,
i am hooking up a hot tub. At first i though of 6/3 Romex for main panel to subpanel attached to house outside, then THHN in 1" conduit another 15 feet to hot tub. But the last 4 feet inside travels in a bay over a finished section of the basement ceiling, so i cannot reach in there to staple/mount the romex, and even if i could, it eventually needs to travel through the wall, and up 2 feet outdoors to subpanel, which would require conduit through the wall and up 2 feet outside. I know i cannot strip the Romex and put into the conduit, but is there a distance limit where this is allowed?

I can extend the conduit into the 4 foot bay from outside, but if i strip the shielding off , the wires are not labeled so not code conforming. Do i need to have a junction box at the start of the 4 foot finished ceiling to terminate the Romex, and start the THHN going the 4 feet inside, and the 2 feet outside, all through the conduit?
What exactly does a junction box look like here? is it just a casing mounted on the joist, and use threaded twist connectors inside? Or does it need some type of termination bars, in and out?
Any help is appreciated.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The junction box can be a standard electrical box of sufficient size based on the gauge and quantity of conductors entering it. Then, appropriate sized wire nuts. You need to use the proper clamps or adapters on the entry to the box.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
The NM-B cable (Romex is a brand name) does not need to be secured/stapled if fished through walls and ceilings.

Generally you would mount a weatherproof junction box on the outside of the house and the NM-B would come in through the back. There you would transition to THWN/PVC to outside panel.
 

WoodenTent

New Member
Messages
26
Reaction score
1
Points
3
Location
Earth
If your conduit doesn't terminate in a panel, box, etc at both ends, then it's not a conduit, it's just a wire protector. As was mentioned, you can go thru your wall, mount an LB there and change to TWHN, the NM-B would be fine going thru the conduit to where you can access it.
 