Rise pressure switch to 60 then motor won't cut off

RoyJ

New Member
Messages
2
Reaction score
0
Points
1
Location
USa
Good morning,

My current surface pump pressure switch is set 35-50
The pump is 100ft from the house then it has to push the water through a softener & an iron filter. By the time water gets inside the house the pressure is pretty low
I raise it to 60 then the pump keeps running unless I drop it back down to 50
Is there any way to raise my pressure to 40-60 without buying new equipment?
If I could get the cut in pressure raised to 40 I think that would make at least a noticeable difference

thank you
 
Good morning,

My current surface pump pressure switch is set 35-50
The pump is 100ft from the house then it has to push the water through a softener & an iron filter. By the time water gets inside the house the pressure is pretty low
I raise it to 60 then the pump keeps running unless I drop it back down to 50
Is there any way to raise my pressure to 40-60 without buying new equipment?
If I could get the cut in pressure raised to 40 I think that would make at least a noticeable difference

thank you
What pressure does it get to? If 57, you might set the pressure switch to cut off at 52 or 53 to give some margin.
 
I have water with lots of sediment and several stages of filters (pH neutralizer, iron filter, carbon, ultrafilter) that kill the flow plus if I draw from the well too quickly the sediment gets worse. I now trickle the water through the filters into a 500 gallon tank and pump straight from there for usage in the house.
 
he pump is 100ft from the house then it has to push the water through a softener & an iron filter. By the time water gets inside the house the pressure is pretty low
Many iron filters require a high flow to backwash, and if they do not get enough flow for backwash, they get blocked up. I think you need to assess your situation, and get ready to spend money.

Get a pressure gauge to look at water pressure in the house during flow conditions. A 0-100psi garden hose thread pressure gauge need not be expensive.
 
Is this now a recent problem, or has it been a long term issue that may have began upon the installation of the water treatment devices?

If it's a recent issue, perhaps there maybe a problem with either the softener or iron filter that is causing flow to be restricted.

Are you able to by-pass the iron filter and softener individually, to determine if there is an immediate improvement in flow and pressure downstream to fixtures when one or the other is by-passed?
 
Is this now a recent problem, or has it been a long term issue that may have began upon the installation of the water treatment devices?

If it's a recent issue, perhaps there maybe a problem with either the softener or iron filter that is causing flow to be restricted.

Are you able to by-pass the iron filter and softener individually, to determine if there is an immediate improvement in flow and pressure downstream to fixtures when one or the other is by-passed?
IF I bypass the iron filter & water filter we have good pressure.
I think we need more pressure, not the 35-50 we have. But that's just my DYI info I've gathered off the forms.
Is there a way to increase my pressure to 4-60?
 
Is there a way to increase my pressure to 4-60?
As Valveman stated above, your existing pump is not capable of building to 60+psi. To achieve higher pressure, you would need to replace the existing pump, or boost pressure after the well pressure tank using an additional inline booster pump.

While I agree, your present 35-50 psi pressure switch settings (should actually be 30-50 to provide 20 psi differential to achieve increased minimum pump run time) are a little anemic, you didn't answer my prior question. Has the downstream pressure always been unacceptably low with the water treatment equipment in-place, or is this a sudden condition, or possibly, one that has gotten progressively worse over time?

IF I bypass the iron filter & water filter we have good pressure.
It then seems the 35-50 psi pressure range is not really an issue.

As asked above, are you able to by-pass each treatment device individually to determine which one is restricting flow?

While the inclusion of water treatment equipment will result in some flow restriction resulting in some pressure reduction, the amount of restriction through a properly sized and functioning system is typically not excessive or usually noticable, particularly if water use is to only 1 fixture.

While you could incur considerable expense to increase the pressure range before the treatment equipment, if there is an issue with one of the treatment devices, you may continue to experience unacceptably low downstream flow (low pressure) regardless. Always best to first diagnose and investigate to determine the cause, so as to not proceed incorrectly based only on a symptom.
 
Every device a valve, pipe size, number of fitting, filter/ size has pressure drop. Pumps are sized by head ( which lenght of pipe, rise of pipe, fittings, devices and gpm). If you had brand, hp and model of pump. Can look at pump curve and tell you how to check the performance of it.
 