Looking to fit new baseboard covers on my combi boiler hydronic system.


Have any of you ever seen these? There is no flap to control heat output. The only part that comes off is that front panel under the top molding. The top part is almost “molded” into the wall if you will. I’m looking for covers that let more heat out.

01E6FB33-3051-4852-BD9C-4BA98F3C4D81.jpeg
 

Fitter30

Well-Known Member
Messages
4,292
Reaction score
778
Points
113
Location
Peace valley missouri
Never seen that type of cover must be as old as the building. To get more heat out of the baseboard need to raise boiler water temp. Baseboard doesn't really start to heat till water temp is 120*. What is the water temperature in and out of the boiler?
 

Csvt18

Member
Messages
32
Reaction score
0
Points
6
Location
Michigan
Never seen that type of cover must be as old as the building. To get more heat out of the baseboard need to raise boiler water temp. Baseboard doesn't really start to heat till water temp is 120*. What is the water temperature in and out of the boiler?

it was 155f. I had to up it to 167f supply as it’s low 20s in the day and low teens at night. Average return is around 150f. I have no clue why. I cleaned all baseboards. No leaks.
 

Csvt18

Member
Messages
32
Reaction score
0
Points
6
Location
Michigan
it was 155f. I had to up it to 167f supply as it’s low 20s in the day and low teens at night. Average return is around 150f. I have no clue why. I cleaned all baseboards. No leaks.


My return temp varies actually. It’s only 5-7 degrees lower when main level is heating. The smallest delta I think due to the boiler being right below that floor.

5-9 delta whey only basements on. And 10-12 when upstairs is on. Also 10-12 delta when all 3 zones are on at once.
 

Csvt18

Member
Messages
32
Reaction score
0
Points
6
Location
Michigan
Normally the td is 20*. What brand and model of boiler just take a pic of tag .Length of baseboard and pipe size.

navien ncb180e.

we have a tri level with 1/2” standard fin baseboards. Never measured total length but every bedroom has it. We have some long runs of 8 feet or so baseboards in every room.
 

Csvt18

Member
Messages
32
Reaction score
0
Points
6
Location
Michigan
navien ncb180e.

we have a tri level with 1/2” standard fin baseboards. Never measured total length but every bedroom has it. We have some long runs of 8 feet or so baseboards in every room.


Measured 105’ of total baseboard in my 2100 sq ft house that’s all 3 floors.
 