Replacing old cast iron boiler with - Bosch SSB, Navien, Lochinvar?
Kingston, NY
Interesting, I'll definitely try changing the outdoor reset, it's ranging from about 145º-155º right now.
As for the condensate, trust me, getting plenty. burning through a 2lb. bag of neutralizer every month. Condensate pump cycles at least three times a day.
Kingston, NY
Have you started dialing in the outdoor reset curve yet? With the NHB boilers it usually does best on both efficiency & comfort by using the return rather than supply temperature for control, and tweaking the outdoor reset to the lowest temperatures that actually keep up with the load. Putting it in to return-temp control mode requires setting the first two positions on DIP SW 2 on the control board to ON (#1), OFF (#2). See p.48 in the manual. Setting it up for cast iron rads with outdoor reset on high volume radiators read how to set up the parameters in section 9.6 (beginning on p.59) Set parameter A to "oRC" to enable outdoor reset mode control (page 59), parameter B to "6" for cast iron (p60). Parameters C & D will need to be tweaked experimentally to dial it in.
If you want use overnight setbacks you might want to set parameter E to speed up recovery from setbacks after the main curve is dialed in a bit.
You can probably leave the rest of the parameters at their default settings unless it exhibits short-cycling behavior during the shoulder seasons when the heat load is low (not very likely with high volume radiators and only two zones.)
With the reset curve adjusted fairly closely it will take a long time for the thermostats to be satisfied, and you can reduce the number of burn cycles per day to a mere handful. The house will stay at a very stable temperature, and the radiators won't change temperature very quickly at all- they'll always be somewhere between warm (or even tepid), and only get really hot when it's actually cold outside. The more time the boiler spends at return water temps of 120F or lower, the more condensing efficiency you'll get out of it. If it's been saving you 40% even without tweaking the curve in, it'll probably save ~50% with the curve tuned more finely, but as importantly, it'll stay comfortable, with no temperature over/under shoots from the burn cycles.
This was immensely helpful, thanks. Turns out a few of the settings were off. It was set for finned tubed baseboard instead of radiators and the outdoor reset was at 14ºF (factory default).
I set the outdoor reset for 11ºF and changed it to radiators.
Will see what that does, thanks again.
Dana
In the trades
It will require dropping the low-temp quite a bit to fully find the sweet spot- a 3F change from 14 down to 11 isn't very much. Drop it to 0F or even -10F, see if it still keeps the house up to temp over night.
You'll probably see a big difference in the condensate volumes with the boiler running entering water temps under 120F most of the day. Without the formal room by room load heat load and radiation analysis it's hard to predict how low you need to set the outdoor reset's low end, or at what outdoor temperature the condensate becomes truly copious, but it will increase when the reset curve is fully dialed in.
Fitter30
Peace valley missouri
All the condensing high efficiency boilers I've seen have a minimum gpm flow through them. How zones are controlled and the use of variable speed pumps have to be addressed. Might have to have a primary secondary loop. Insulation pay for it now or pay your utility company forever.
Fitter30
Without a room load how are you sizing the new radiators? Are you totally repiping the system? Have you checked with your gas company for any or the electric company for any window ,insulation rebates?