Ok, good to have exact measurements.
For the recovery period you give after the showers ended, I calculate that out as somewhere between 94k-108k BTU/hr heat output from the boiler into the indirect (the range coming from whether your time period between temperate measurements was closer to 7 or to 8 minutes). Right around the 106k BTU/hr rating of your boiler, which also lines up with the 100% burner modulation on the display. Ok, things appear to be working correctly just as you say.
What's eluding me is this. In the 8 minute period your son was in the shower, the tank dropped 41F with the burner at maximum output. My math should be checked, but even at worst- case 32F incoming water temps, this requires something like 5+ GPM inflow.
Your daughter's shower, on the other hand, comes out somewhere in the 1.5 GPM range.
Did the kids use the same shower? Or perhaps did another appliance like a clothes washer also draw off the tank during your son's shower?
For the recovery period you give after the showers ended, I calculate that out as somewhere between 94k-108k BTU/hr heat output from the boiler into the indirect (the range coming from whether your time period between temperate measurements was closer to 7 or to 8 minutes). Right around the 106k BTU/hr rating of your boiler, which also lines up with the 100% burner modulation on the display. Ok, things appear to be working correctly just as you say.
What's eluding me is this. In the 8 minute period your son was in the shower, the tank dropped 41F with the burner at maximum output. My math should be checked, but even at worst- case 32F incoming water temps, this requires something like 5+ GPM inflow.
Your daughter's shower, on the other hand, comes out somewhere in the 1.5 GPM range.
Did the kids use the same shower? Or perhaps did another appliance like a clothes washer also draw off the tank during your son's shower?