The Bosch combi units are almost always a terrible fit for reasonably insulated average sized houses. The minimum input of the 131 is 36,000 BTU/hr, which can be problematic even for domestic hot water temperature control at low flow. But it would also require about 170-180' of fin-tube baseboard to emit that much heat at condensing temperatures without cycling on/off. The Greenstar Combi 100 is better, but at ~25,000 BTU/hr in still needs 110-120' of baseboard (per zone) to operated at condensing efficiency without cycling.
If it HAS to be a combi boiler, Navien's combi boilers have much better turn down ratios, and minimum firing rates that can SOMETIMES work well in average sized homes.
It's fine if the capacity at
maximum-fire is way oversized for the whole house heat load, but not so great if the
minimum-fire output is also oversized for the heat load and TERRIBLE if the minimum fire output is oversized for the
radiation. To avoid that, measure up all of your radiation (zone-by-zone, if multi-zoned) and report back (or
run the napkin-math yourself.)
If you have a heating history on the place,
run a fuel-use based load calc to ballpark the actual 99% design heat load using the old boiler as the measuring instrument.