I am reviewing the one document done by the last professional who installed the Warmboard manifold 18 months ago. He walked off the job with the heat not running leaving me to hire another person to install new valves to bleed the air out of the system. Two of the three Honeywell Zone Valves also have bad end-switches - (Yes the original contractor did get paid without the heat running in the house).

The document (attached) left by the original contractor has the instructions to "Pull Check Valve" out of the two recirculation pumps (Grundfos UPS15-58FC). However, I don't see the "Check Valve Removed" label on the name plate of the pump. So I don't know if it was pulled or is still installed. The larger question is what is the reason WHY the check valve would be pulled out of the two pumps. The indirect has its own Taco-007-ZF8-9 pump.

Trying to determine if I can re-use the pumps when I upgrade the boiler to a mod-con and move all of the CH over to the manifolds (Rehau Pro-Balance).
 

Attachments

  • CurrentPiping.JPG
    CurrentPiping.JPG
    49.7 KB · Views: 636

BirchwoodBill

New Member
Messages
18
Reaction score
0
Points
1
Location
Birchwood Mn.
Interviewing contractors for replacement project. was told it is common practice when using a circuit with zone valves. It cuts down on flow loss.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
That may be a common practice and a common rationale for it, but it's not the right thing to do. Most systems are way over-pumped to begin with, and removing the check valves causes back-flow on other zones when just one pump is running.
 

NY_Rob

In the Trades
Messages
317
Reaction score
26
Points
28
Location
New York
If your thermostats control your zone valves directly (which is common/accepted practice in small-simple systems), the zone valves stay open if they were on a heat call when the DHW priority call came in. You will get reverse flow in that situation if the flo-checks were removed.
I'm not a big fan of the IFC (built in the the pump) type flo-check, I prefer the flange or inline type for numerous reasons.
 