My system has a supply manifold with three circulator pumps and isolation valves. There is a return manifold with a boiler drain and isolation valve for each zone.
From reading the archived posts in this forum and other forums, it's my understanding that to purge all the air from my boiler, I need to do the following:
1. Shut the isolation valves for all the zones on the return side and supply side.
2. Turn power off to boiler and circulation pumps.
3. Working only one zone at a time, do the following:
a. open the isolation valve on the supply side for the zone.
b. put a hose on the correct drain and put end into bucket
c. open drain thereby letting water into bucket
d. open fast-fill valve (actually lever), keeping an eye on the boiler pressure gauge to make sure it doesn't exceed 40 PSI.
e. fill bucket until no more air bubbles come out.
Repeat #3 for the next zone.
On my system, I have slant-fin baseboard radiators. They have bleeder valves. Is it necessary at all to use these bleeder valves if you purge the air via the drains? The reason that I ask is that on most of my baseboards, you cannot take off the cover and expose the bleeder valve. It seems that I would need to put some sort of absorbent rag around it because the bleeder valve is not oriented in the correct direction to use a small container to collect the water.
So I wonder if one can purge the system of air by using the drain valves on the return and not use the radiator bleeder valves.
What do plumbers use to open the bleeder valves? A screwdriver?
From reading the archived posts in this forum and other forums, it's my understanding that to purge all the air from my boiler, I need to do the following:
1. Shut the isolation valves for all the zones on the return side and supply side.
2. Turn power off to boiler and circulation pumps.
3. Working only one zone at a time, do the following:
a. open the isolation valve on the supply side for the zone.
b. put a hose on the correct drain and put end into bucket
c. open drain thereby letting water into bucket
d. open fast-fill valve (actually lever), keeping an eye on the boiler pressure gauge to make sure it doesn't exceed 40 PSI.
e. fill bucket until no more air bubbles come out.
Repeat #3 for the next zone.
On my system, I have slant-fin baseboard radiators. They have bleeder valves. Is it necessary at all to use these bleeder valves if you purge the air via the drains? The reason that I ask is that on most of my baseboards, you cannot take off the cover and expose the bleeder valve. It seems that I would need to put some sort of absorbent rag around it because the bleeder valve is not oriented in the correct direction to use a small container to collect the water.
So I wonder if one can purge the system of air by using the drain valves on the return and not use the radiator bleeder valves.
What do plumbers use to open the bleeder valves? A screwdriver?