proper AC condensate connection under sink

Users who are viewing this thread

Cjccmc

Member
Messages
47
Reaction score
1
Points
8
Location
California
Hi,

Today I noticed water near the outside of my AC unit leaking about where the coils are located.
After a little investigating I found the condensate line did not allow water to flow. I cleared the run from the AC to the connection at the drain under my bathroom sink.

What I noticed is that there is not much room for the condensate to enter the drain as there is a (gray) pipe above it that extends past the condensate tap. See pic. Is that gray pipe supposed to go down as far as shown or should it end above the condensate nipple?
annotated drain pic under sink.JPG
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
Cut the grey pipe just above the stub for the condensate line.
Make sure you tighten your connection so that the trap doesn't drop. I would put something under the trap for support (something like a tile or a brick, depending on the space).
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
NO COMPANY EVER made a piece like that so someone cobbled it together. You have to cut the sink's tailpiece so it is above the condenate opening.
 