if i understand correctly the aquastat used on a boiler with a coil keeps the boiler water at a certain temp so when u need hot water it does not have to wait to get hot water

lately hot water seeems to take a while to come....i had the aqustat at 160 and raised to 170

it has been very cold here lately....

would going higher on the aquastat be ok?

or i'm wondering if its a problem with the aquastat itself

last year i remeber the hot water meter o the hot water pipe would stay round 120 ....now it stays around 80-90 average

the boiler and coil is 1 year old
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
A boiler coil for domestic hot water needs the boiler to be fairly hot to work well, especially in the winter when the incoming cold water can approach freezing. Often, the thing is designed for 180-200 degrees. Yes, you can adjust it up, but it will increase fuel use, but you'll have hotter water.
 