Pressure Loss Calculation

kybob

New Member
Messages
18
Reaction score
0
Points
1
Location
Kentucky
In the midst of determining 3/4 vs 1/2 for a two shower head situation where both would be on at the same time and assuming the higher limits of the permitted flow (2.5 GPM each). This will be a home run from a manifold. There are small things such as the shower line that are not accounted for yet.

- Am I in the ballpark for the pressure loss estimations?
- Will 3/4" with 3/4" valve make a noticable difference?
- Will 3/4" with 1/2" valve (reducing at shower valve) make a noticable difference?
 

Attachments

  • shower.jpg
    shower.jpg
    36.7 KB · Views: 251

John Gayewski

In the Trades
Messages
5,236
Reaction score
1,714
Points
113
Location
Iowa
In the midst of determining 3/4 vs 1/2 for a two shower head situation where both would be on at the same time and assuming the higher limits of the permitted flow (2.5 GPM each). This will be a home run from a manifold. There are small things such as the shower line that are not accounted for yet.

- Am I in the ballpark for the pressure loss estimations?
- Will 3/4" with 3/4" valve make a noticable difference?
- Will 3/4" with 1/2" valve (reducing at shower valve) make a noticable difference?
How many feet of pipe?
 

John Gayewski

In the Trades
Messages
5,236
Reaction score
1,714
Points
113
Location
Iowa
At 2.5gpm (your shower head likley won't even give you that much) 1/2" pex looses 14ft of head per 100 ft. of pipe. 3/4" looses 4 ft of head per 100 ft.

So your gonna get roughly 3.5 times more pressure with 3/4".

Will it make a noticeable difference? Probably not, not unless the run is long excessively long or your pressure is excessively low.
 

kybob

New Member
Messages
18
Reaction score
0
Points
1
Location
Kentucky
How many feet of pipe?
I've uploaded an image with details on each section. I estimated ~8 PSI loss up to the manifold then my optionality. I redid the calculations with uponor chart for 120 degreee (https://www.uponorengineering.com/~...ressure loss charts.ashx?version=062520180400) and got these numbers. Using 4gpm based on 80/20 hot to cold ratio.

Initial: 60 PSI - 8 PSI loss
Option A (1/2): 4gpm 6.59 psi/100ft * (40ft/100ft) = 2.64 psi loss est final 49.4 PSI
Option B (3/4): 4gpm 4.29 psi/100ft * (40ft/100ft) = 1.72 psi loss est final 50.28 PSI

Does that look correct? If so this seems negligble as long as I can reasonably get that flow from 1/2.
 

wwhitney

In the Trades
Messages
7,377
Reaction score
2,141
Points
113
Location
Berkeley, CA
Broken link.
Initial: 60 PSI - 8 PSI loss
Option A (1/2): 4gpm 6.59 psi/100ft * (40ft/100ft) = 2.64 psi loss est final 49.4 PSI
Option B (3/4): 4gpm 4.29 psi/100ft * (40ft/100ft) = 1.72 psi loss est final 50.28 PSI
One of those numbers is wrong, the ratio should be over 5.
Does that look correct? If so this seems negligble as long as I can reasonably get that flow from 1/2.
I get 4 gpm in 1/2" PEX = 7.2 ft/sec, under the Uponor recommendation of maximum 8 ft/sec.

Cheers, Wayne
 

kybob

New Member
Messages
18
Reaction score
0
Points
1
Location
Kentucky
Broken link.

One of those numbers is wrong, the ratio should be over 5.

I get 4 gpm in 1/2" PEX = 7.2 ft/sec, under the Uponor recommendation of maximum 8 ft/sec.

Cheers, Wayne
Shoot - here is the correct link https://us.v-cdn.net/5021738/uploads/FileUpload/70/d215f960a1b9a3ad6208c62fc26891.pdf.

Am I misreading the table? for 1/2... 4 gpm is 4.29 PSI /100 feet @ 120F.I have a 40 ft run so 6.59 *.4 = 2.64.

Side note - based on this calculator I could in theory draw up to 4.61gpm via a 1/2 line before seeing issues?
 

wwhitney

In the Trades
Messages
7,377
Reaction score
2,141
Points
113
Location
Berkeley, CA
Last edited:

kybob

New Member
Messages
18
Reaction score
0
Points
1
Location
Kentucky
Yes, you are misreading the table. 4 gpm in 1/2" PEX at 120F is 19.21 PSI / 100 ft. While 6.59 PSI/100 ft is the entry for 4 ft/sec or 2.21 gpm in 1/2" PEX at 120F.

Cheers, Wayne
Thanks Wayne - I've been starring at too many tables for too long.

That appears to put 1/2 at final velocity ~42 psi +/- 5 and 3/4 at 48.2 +/- 5. My guess is no, but will that be a noticeable difference when running two shower heads on a 1/2 valve?
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.