Pipe insulation near boiler

Users who are viewing this thread

Theodore

Member
Messages
127
Reaction score
4
Points
18
Location
New York
I've a 147k btu hot water boiler for hydronic heat system. Most of the domestic hot water pipes and even the heating pipes have rubberized or foam pipe insulation on them... the kind you buy at big box stores manufactured by Everbilt, Armaflex, etc. But it all stops about 4ft from the boiler. Can this be used around the boiler or do I need to use something more flame-retardant? If so, can you make any suggestions? Thanks
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Most of the cheap foamy stuff isn't even rated for typical 180F hot water plumbing, let alone the near-boiler plumbing next to flues, but can usually be used on low-temp hydronic distribution plumbing to radiant floors, low-temp panel radiators, etc.

Check the operating temp specs of any product you use against the system's operating temp.

1" - 2" wall fiberglass commonly used on steam piping works on just about any near-boiler plumbing. Stay away from the crummy 1/2" wall paper-clad good sold at box stores though- 1" would be the minimum thickness to be really useful on near-boiler plumbing that's running in excess of 160F. There are multiple places to get the real stuff online, at prices for 1" fiberglass thickness substantially better than you can get for the crummy half-inch box-store stuff.

382368602_364.JPG
 