P trap in laundry room floor drain connection
Toothdriller
phoenix
I am trying to figure out how to lay out a floor drain in the laundry room.
Would the lay out in the first picture work? it would connect to the wet drain after the laundry. If this can be done, what fitting would be used to connect the floor drain p trap to horizonal drain and at what angle.
I am thinking layout 2 is the correct way but would layout 1 work?
I also attached a 3rd picture which the adjacent bathroom with vent connects if that makes a different
Any help or suggestion would be gladly appreciated. Thanks!
.. this under concrete slab
wwhitney
Berkeley, CA
Looks like Pheonix is under the IPC. In which case either layout would be OK, with all the drains sized at 2".
Layout 1 would be a "combination waste and vent system," IPC section 915. I'm not so familiar with that section, but just the pipe from the floor drain p-trap to the wye is the combination waste and vent. 2" is sufficient, as a floor drain is 2 DFUs.
https://up.codes/viewer/colorado/ipc-2018/chapter/9/vents#915
Layout 2 would be a "common vent connected at different levels," IPC section 911.3. 2" is sufficient as the upper fixture, the laundry standpipe, is 3 DFUs.
https://up.codes/viewer/colorado/ipc-2018/chapter/9/vents#911.3
Cheers, Wayne
Toothdriller
phoenix
Cheers, Wayne
I was under the impression a p trap always has to eye or see a vent and so essentially connect with a sanitary t. So a WYE laying flat on the horizontal will work?
also, In picture 3 for the adjacent bathroom, will that work based on
wwhitney
Berkeley, CA
Conventional dry vents are often connected via a sanitary tee, which is convenient when you want to simultaneously turn the drain down while taking off the vent. They can also be connected with a vertical combo, when you want the drain to stay horizontal while you take off the vent.
Horizontal wet venting and this combination waste and vent system do allow venting via a horizontal wye. They have sizing rules to ensure that the horizontal pipe should not fill up up with water, so the top of the pipe provides a pathway for the requisite vent air.
Cheers, Wayne
Toothdriller
phoenix
Cheers, Wayne
Thanks for the help so far Wayne!
So for instance, I can have wet vents with WYE for the bath, toilet, and sink as shown? Assuming 3" wc, 2" tub, 2" sink, and 3" horizontal ? Assuming IPC codes. Will this work?
wwhitney
Berkeley, CA
Not quite. Two issues:
(1) In a horizontal wet vent, any horizontal pipe that is a vent has to be wet, not dry. That mean that some fixture washes through it. Otherwise, at the wet/dry junction on that vent, solids could back up occasionally, and with nothing to wash them down, they could accumulate. So the red segment between the toilet wye and the blue vent is not a compliant way to attach the vent connection to the horizontal wet vent.
(2) The lavatory p-trap is much higher than the tub p-trap or the toilet outlet. And the lavatory drain need to be vented before the drain turns downward, the vent under the floor is too low. So you need to provide a regular dry vent for the lavatory, typically with a san-tee. And once you do that, the lav dry vent can serve to wet vent the toilet and bathtub.
Under the IPC, you can use 1-1/2" for everything except the toilet drain (and drains combined with the toilet drain).
Cheers, Wayne
So for instance, I can have wet vents with WYE for the bath, toilet, and sink as shown? Assuming 3" wc, 2" tub, 2" sink, and 3" horizontal ? Assuming IPC codes. Will this work?[/QUOte
sorry duplicate posting feel like an idiot website said there was an error and then went and repeated my posts sorry all
Toothdriller
phoenix
Cheers, Wayne
Toothdriller
phoenix
So something like this? Where the toilet goes to vertical dry vent. Then long 90 to horizontal? The sink would have its own dry vent but still drain to horizontal.
Toothdriller
phoenix
Cheers, Wayne
Flow toward bottom of the picture, right? How about this?
Toothdriller
phoenix
Yeah. Flow is going down stream. I have the existing vent on the back wall that goes straight up to roof. That is why I'm trying to tie it in. Anyway yo tie that in and make it still work?
Toothdriller
phoenix
I have existing vents to ceiling as shown. One is the sink which goes to a san t to roof. The other I'm trying to figure out how to tie in the system.