Oil Funance Chimney issue

Users who are viewing this thread

theMezz

New Member
Messages
29
Reaction score
0
Points
1
Location
Central NY
A chimney to a oil furnace collapsed, and I see the local heating contractor installed a power vent http://s3.pexsupply.com/manuals/1260541270124/20400_PROD_FILE.pdf with am exhaust pipe that goes outside and just about the ground (not a real chimney)

Anyone hear of this before? It's a high snow area - won't it get covered with snow? They had to shovel away 4 foot of snow outside to install this.

Is that code compliance??

Thank You
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Very very coommon practice. Make sure to follow the installation instructions for distances to windows, the ground, doors and such.
 

theMezz

New Member
Messages
29
Reaction score
0
Points
1
Location
Central NY
here is a photo

heat.jpg
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The exhaust and intake usually are supposed to be above the snow level. It depends on the specifics of the installation manual. As noted, it is also very important about where it terminates verses things like door, windows, and other intakes and exhausts. This is all spelled out in some detail in the specific device's installation instructions.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
The exhaust and intake usually are supposed to be above the snow level. It depends on the specifics of the installation manual. As noted, it is also very important about where it terminates verses things like door, windows, and other intakes and exhausts. This is all spelled out in some detail in the specific device's installation instructions.

It also depends on local code. This wouldn't pass code anywhere in MA that close to the ground due to snowpack related issues, but it might be allowed in TX. I'd be suprised if an inspector would sign off on it that way in NY. Buried in snow next to the house the exhuast will find it's way under siding & sheathing, can present a very serious health hazard, even if the location met all other clearance requirements to operable windows & doors, air intakes, etc. .
 

theMezz

New Member
Messages
29
Reaction score
0
Points
1
Location
Central NY
Amazingly enough it was installed by a heating company that is very popular and has been around for many years. WTF !
 