Oil Burner Tankless Coil Problems

Users who are viewing this thread

tim_

New Member
Messages
2
Reaction score
0
Points
1
Location
Maine
I have a tankless coil water heater in my burner. I'm noticing when in the shower, the water will start hot, then drop in temp, but after waiting about 2 minutes, the temp will rise back up again. The Boiler is also heating my hydronic baseboard heat. I've confirmed this happens without any other sinks/appliances in use. The coil is old, but not leaking.

any ideas on what it could be? trouble shooting steps?

Thanks
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
The water sitting at idle in the coil is at whatever temperature the boiler happens to be, which is "hot enough". When the flow starts that first slug of water is hotter than what immediately follows, since the slug of cooler water doesn't heat up to the full boiler temp on it's way through. As the burner kicks on the boiler temp rises enough so that the output of the coil is at a decently hot domestic hot water temperature. If the low-limit on the boiler isn't high enough or the coil is liming up a bit that delay will be worse.

Most tankless coils can deliver at least OK hot water performance at 150Flow-limit when new, but may have to be bumped up to 160F or higher over time (and you say this one is "old".) What are your aquastat settings?

Bumping up the temperature may be a reasonable short-term fix, but it also increases the standby losses of the boiler, for lower net efficiency. It may or may not be worth de-liming the coils. Sometimes de-liming uncovers pin-hole leaks that had been scabbed over and sealed by lime deposits, causing the system to slowly over-fill until it's in an over-pressure condition, but if you want to give it a shot, be prepared with a "plan -B" if that happens.

Plan-B would be to replace the coil, but that's not necessarily the best solution if you'll be living there for years/decades. An indirect hot water tank operated as the priority zone off the boiler allows you to lower the idling and average temperature of the boiler, lowering the standby losses, and if coupled with a heat purging economizer control can lower the number of ignition cycles and overall burner-on time. Those controls still have some benefit even when using a tankless coil for the hot water, but the idle temperature would still have to be high enough to deliver reasonable hot water performance with the coil, rather than heat purging the boiler down to 140F on heating calls before engaging the burner.
 

tim_

New Member
Messages
2
Reaction score
0
Points
1
Location
Maine
The water sitting at idle in the coil is at whatever temperature the boiler happens to be, which is "hot enough". When the flow starts that first slug of water is hotter than what immediately follows, since the slug of cooler water doesn't heat up to the full boiler temp on it's way through. As the burner kicks on the boiler temp rises enough so that the output of the coil is at a decently hot domestic hot water temperature. If the low-limit on the boiler isn't high enough or the coil is liming up a bit that delay will be worse.

Most tankless coils can deliver at least OK hot water performance at 150Flow-limit when new, but may have to be bumped up to 160F or higher over time (and you say this one is "old".) What are your aquastat settings?

Bumping up the temperature may be a reasonable short-term fix, but it also increases the standby losses of the boiler, for lower net efficiency. It may or may not be worth de-liming the coils. Sometimes de-liming uncovers pin-hole leaks that had been scabbed over and sealed by lime deposits, causing the system to slowly over-fill until it's in an over-pressure condition, but if you want to give it a shot, be prepared with a "plan -B" if that happens.

Plan-B would be to replace the coil, but that's not necessarily the best solution if you'll be living there for years/decades. An indirect hot water tank operated as the priority zone off the boiler allows you to lower the idling and average temperature of the boiler, lowering the standby losses, and if coupled with a heat purging economizer control can lower the number of ignition cycles and overall burner-on time. Those controls still have some benefit even when using a tankless coil for the hot water, but the idle temperature would still have to be high enough to deliver reasonable hot water performance with the coil, rather than heat purging the boiler down to 140F on heating calls before engaging the burner.
Thanks! I do think long term I should get an indirect hot water tank, it's a home I recently purchased and the condition of the coil came up during inspection. Since it's pretty corroded, the plumber that did the cleaning said it would be about the same cost to replace as an indirect tank install. For now, I was wondering why it had the potential to be hot, but would go through cold cycles. I'll try bumping up the low limit up for now.
 