Oil boiler high/low temp

Users who are viewing this thread

jmoser201

New Member
Messages
5
Reaction score
1
Points
3
Location
Pottstown PA
Recently moved into a home that has an oil boiler which provides hot water for baseboard heating and an indirect hot water tank. I just had a plumber/hvac guy out to replace the expansion tank and he noticed the Honeywell high/low setting which is currently set at 180/160 with a diff of 10. He said the low was set too high and put it at 120. I researched and that seems way too low for an oil boiler, but I’m not an expert. Does anyone know what the best settings would be for my system? It’s a peerless boiler from 1989. My concern is that 120 will cause condensation

D04A9695-CA26-402E-93FF-92C07356CFC9.jpeg
E9D9B7E6-3B89-4DC6-B5AE-D82E41A740EF.jpeg
BD6BA489-8555-4A0B-9D56-D3066F55CD19.jpeg

V3XyTWm

GM7wq3C

NSMRBMv
 

Fitter30

Well-Known Member
Messages
4,291
Reaction score
777
Points
113
Location
Peace valley missouri
Leave it at the 180/ 160. Might want a outdoor reset control ( varies the water temp by outdoor temp). Minimum return water temp 135* for your boiler
 

John Gayewski

In the Trades
Messages
4,324
Reaction score
1,319
Points
113
Location
Iowa
That type of boiler should only be set with a 140 min. Anything lower will hasten the boilers life dramatically.
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
might need it, but I guess it’s been set up without one since 1989. So I should leave it at 160/180?

Just because it is WRONG doesn't men it should be left like that BUT do what you want .. As long as you were told then you took full responsibility
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Appreciate the feedback! Not sure what the hvac guy I had out was thinking with setting it at 120.



The "Guy" was possibly thinking about scald protection for a shower


People read various codes and have no idea what it means as it very ambiguous to the non professional
 

Fitter30

Well-Known Member
Messages
4,291
Reaction score
777
Points
113
Location
Peace valley missouri
T
The "Guy" was possibly thinking about scald protection for a shower


People read various codes and have no idea what it means as it very ambiguous to the non professional
Their is a taco control and sensor on the dhw tank and wiring back over to boiler.
 