Occasional bad smell from pipes and under kitchen sink. Is the air admittance vent and plumbing setup correct and "to code " for NC. right?

Gary Caiola

New Member
Messages
1
Reaction score
0
Points
0
Location
North Carolina
What I think is called an AAV (air admittance vent) is at the top of the center stack in the photo. Is anything wrong with the installation?

2 notes:
1- I swapped the disposal to the opposite side of sink several years ago. I don't remember why, but am guessing my wife wanted it on the other side.
2- I no longer live in the house but still own it and rent it out. The tenants claim there's an occasional foul smell from above and below the sink. However I have never noticed it. To appease her, I've poured baking soda then white vinegar thru both sides of sink drains, and let it perk for 10 min before rinsing, to minimize any smell from sludge build up in P traps or anything else. Ive also cleaned out the drain line fromdishwasher that feeds into the disposal.

The primary tenant is also particular about many other things. I'm sensitive to smells also, but have not noticed anything, but she claims to.
Her husband seems like the type of person who would just agree with her regardless of whether he smells anything or not.

First, I want to be sure it's done properly. And second, that it's done in a way to prevent the smells she claims she detects.

I'm assuming that AAV is there for a reason, and that I cannot just tape a bag over it or seal it up as a prevention for possible gases.

Thanks a bunch for any feedback.
 

Attachments

  • Screenshot_20260714_235415_Photos.jpg
    Screenshot_20260714_235415_Photos.jpg
    60.4 KB · Views: 0
Last edited:
An AAV is designed to allow air in, not out, so it shouldn't be a source of smells, unless it has failed.

The plumbing coming out of the disposal is not correct. You've created a very deep and sinuous trap, and there is standing water in the disposal all the time. You should rebuild all the tubular and part of the vertical Schedule 40 at the rear, so that the tubular can enter the vertical portion at a lower elevation. Might as well change the AAV while you are at it. May need to replace the disposal if it's been damaged by the standing water.

When you rebuild it, you have the choice of using two traps like you currently have (in which case the vertical portion would have two stacked san-tees), or just one trap, which is more usual.

Cheers, Wayne
 