I'm replacing all the appliances, the cabinets, other stuff in a small 1950's-era kitchen. The basement ceiling is rather "crowded" with cables, plumbing, etc., so I'm trying--when safe--to re-use some of the cable runs from the updated panel to the kitchen.

The existing cooktop has a 10-3 NM w/ground cable running to a 30A two-pole breaker in the panel. I'm going to remove the cooktop and put a dishwasher in that general area.

My question: can I use the existing cable run as a dedicated circuit, cap off the red wire, and run it to a single pole 20A breaker?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
You can use a larger cable to run a lower powered unit as long as the CB you use is rated to accept that size wire. I'd cap off the unused wire rather than cutting it back, but then, I'm not an electrician!
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
You would have the option to put in 2 120 volt outlet circuits. You could run the microwave oven while running some other high-power device. To do that, you should use a 2-pole breaker. Don't forget to account for using GFCI. There are 1-pole and 2-pole GFCI breakers.
 