New Navien NCB-180E - Sanity Check

Users who are viewing this thread

Jac04

Member
Messages
139
Reaction score
3
Points
18
Location
Connecticut
I recently had a Navien NCB-180E (14ooo Btu/hr min fire) installed to replace a Navien CH-180 (16000 Btu/hr min fire) that had a heat exchanger failure.

The old CH ran well, and heated the house well. My only issue was that I had to manually adjust the supply temperature since none of the ODR curves seemed to work for me.

Last night was the first time that we ran the new NCB unit for heat, and it’s acting a little different than the old CH. The old CH would always run continuously during a call for heat, but the new NCB will cycle on a call for heat.

Example, With a supply set point of 115F, and outdoor temp about 35F:

The old CH would fire and remain firing 100% of the time on a call for heat. Burn times were typically about 10-15 minutes, and supply temperature would typically creep up above the 115F set point to about 125-127F before the t-stat would be satisfied and end the call for heat. From my observations, the CH had a non-adjustable hysteresis of +/- 15F (i.e.: for setpoint = 115F, the burner “on” temp would be 100F and the burner “off” temp would be 130F).

Now for the new NCB unit. My custom ODR curve has the supply setpoint at 114F for 35F outside temp. The call for heat lasts indefinitely, but the burner keeps cycling. It cuts off at 118F and it doesn’t re-fire until it gets down to 109F. It just keeps doing this and the t-stat is never satisfied.

According to the Navien manual, the default burner “off” setting is 4F above the setpoint, and the default burner “on” setting is 5F below the setpoint. This is why I am seeing the 109F to 118F swing with a setpoint of 114F.

Now for the sanity check.

My plan was simply to bump up the burner “off” setting to 10 – 15F. At 114F supply, I know that the unit is putting out more heat at minimum fire than I am putting into the house, so the supply temp is going to continue to rise. My thought is to let the supply temp slowly rise 10-15F above the set point which will 1) keep the burner firing, and 2) satisfy the thermostat.

Does this make sense?
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
That approach should work just fine. The way it is now your average water temp during a call for heat is 114F, but it's not spending enough time at the high end of it's hysteresis range to satisfy the thermostat.

If you open up the hysteresis it'll guarantee longer burns, and spend enough time above the ODR setpoint to satisfy the call for heat.

You could also tweak the ODR up a few degrees to get it to satisfy the thermostat even with the narrower temperature band, but it would probably still cycle a bit during long calls for heat.

Either way is fine, but establishing a longer minimum burn time for fewer burn cycles is nicer to the equipment.

In a perfectly tuned system with sufficient modulation range you could tweak the ODR to where it ran a 100% duty cycle and never satisfied the thermostat, but always kept up with the load.
 

Jac04

Member
Messages
139
Reaction score
3
Points
18
Location
Connecticut
Follow-Up:

I increased the burner "off" temperature from 4F to 15F. What a difference it makes, especially at higher outside temps (40's). No more bouncing between the burner "off" and "on" limits. For example, I bumped up the heat from 68 to 70 this morning and had a nice 80 minute run with the supply temp slowly increasing from 114F to 126F over that time.
 