I installed a new Slant/Fin Intrepid TR-30 1.10gph boiler this past weekend. When I fired it up, it ran beautifully for about 5 minutes when it started rumbling and flapping the damper. When I opened the sight door, it improved and the damper stopped flapping, but I could feel hot air puffing out of the door. It also showed no draft over the fire and virtually none in the stack.
Since the boiler I just replaced showed similar draft numbers (although it ran well), I immediately suspected a plugged chimney. I had a chimney company come out today and clean the flue and install a cap. They said it wasn't that bad. Uh-oh Andy..
I re-fired the burner (Beckett AFG) and the problem is still there after the flue cleaning. I shut it back down, removed the damper from the flue T, and put a piece of paper over the damper opening. With the burner off, I could feel an ever so slight suction with the paper. When I started the boiler again, the paper started flapping like the damper door did.
I then wondered if the boiler had fouled and sooted up during the first fire so I pulled the top off, and it's as clean as a whistle. I then ran it with out the flue and I can see the flame down through the sections, but even when running it with no flue pipe on top, there is still hot air backing out the sight door.
The settings on the AFG are those that Beckett and Slant recommend for that burner, and I tried opening and closing the shutters, but it doesn't want to run smoothly.
I know it can because it did for the first 5 minutes.
As far as the flame, it's hitting the back target at what would appear to be half the flame distance. The flame curls back around and it seems like the flame tendrils are almost making it back to the burner, like it's got a honking big nozzle at a narrow angle. It's a 80 degree "W" Delavan (or that's what it's supposed to have been shipped with.
Any chance the new nozzle crapped out after 5 minutes? Further info, I bought the boiler about three years ago and it's been sitting wrapped in plastic sitting in the crate in my basement until this week. There is QC paperwork on the burner that shows that the burner was test run. Maybe something happened to the nozzle after sitting for three years?
I have another nozzle I can try if anyone thinks that might help.
I'm stumped and am willing to listen to any suggestions.
John
Since the boiler I just replaced showed similar draft numbers (although it ran well), I immediately suspected a plugged chimney. I had a chimney company come out today and clean the flue and install a cap. They said it wasn't that bad. Uh-oh Andy..
I re-fired the burner (Beckett AFG) and the problem is still there after the flue cleaning. I shut it back down, removed the damper from the flue T, and put a piece of paper over the damper opening. With the burner off, I could feel an ever so slight suction with the paper. When I started the boiler again, the paper started flapping like the damper door did.
I then wondered if the boiler had fouled and sooted up during the first fire so I pulled the top off, and it's as clean as a whistle. I then ran it with out the flue and I can see the flame down through the sections, but even when running it with no flue pipe on top, there is still hot air backing out the sight door.
The settings on the AFG are those that Beckett and Slant recommend for that burner, and I tried opening and closing the shutters, but it doesn't want to run smoothly.
I know it can because it did for the first 5 minutes.
As far as the flame, it's hitting the back target at what would appear to be half the flame distance. The flame curls back around and it seems like the flame tendrils are almost making it back to the burner, like it's got a honking big nozzle at a narrow angle. It's a 80 degree "W" Delavan (or that's what it's supposed to have been shipped with.
Any chance the new nozzle crapped out after 5 minutes? Further info, I bought the boiler about three years ago and it's been sitting wrapped in plastic sitting in the crate in my basement until this week. There is QC paperwork on the burner that shows that the burner was test run. Maybe something happened to the nozzle after sitting for three years?
I have another nozzle I can try if anyone thinks that might help.
I'm stumped and am willing to listen to any suggestions.
John
Last edited: