Neutral and Ground Bus Mixed

Users who are viewing this thread

Todd Groendyke

New Member
Messages
4
Reaction score
0
Points
0
Location
Georgia
Hello: I recently bought a 1950's house. I was examining the electrical panel and it looks like neutral and ground lines are mixed in the the neutral and ground bus. Some neutral are on the ground bus, some ground on the neutral, etc. Is there any reason for doing this? Is it a problem? Should I leave it alone or switch all the neutrals and grounds to their proper bars?

Thanks,

Todd

neutralground.jpg
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Are you going by wire color ?

It looks a bit mixed up to me.

If you update it you should bring it up to code.

Older homes did not have a safety ground.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
That looks like the service panel or I would be more correct if I stated this looks like the service disconnecting enclosure and if my assumption is correct and the two terminal bars are bonded together and to the enclosure there is no problem with the panel.
 

Todd Groendyke

New Member
Messages
4
Reaction score
0
Points
0
Location
Georgia
These photos might show it a little better. My main concern is that neutrals (white) and grounds (bare copper) seemed to be mixed on these bars. Shouldn't all the neutrals be on the neutral bar and all grounds on ground... or does it matter? Or is there a reason to mix them?
Ground.jpgNeutral.jpg
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
There is NO separate neutral or ground bar in that main panel. Both bars serve BOTH purposes.
It is FINE.
 

Murphy625

Member
Messages
161
Reaction score
0
Points
16
Location
Michigan
If the house was built in the 1950's, that panel is not the original and has already been updated. Looks fairly new to me.

I would almost go out on a limb to say that the panel was updated just to sell the home. Judging by the lack of oxidation, dust, debris, etc, I would say that panel was installed within the past 5 years.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
These photos might show it a little better. My main concern is that neutrals (white) and grounds (bare copper) seemed to be mixed on these bars. Shouldn't all the neutrals be on the neutral bar and all grounds on ground... or does it matter? Or is there a reason to mix them?
View attachment 21291View attachment 21292


That is a much better picture.

It looks fine.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Both bars are tied together via the factory strap so they are logically the same bar.

Other issue is that neutrals are sharing lugs. They should be on their own. Grounding wires can share if mentioned on the panel label.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Both bars are tied together via the factory strap so they are logically the same bar.

Other issue is that neutrals are sharing lugs. They should be on their own. Grounding wires can share if mentioned on the panel label.


Good point. I did notice that.

There were spares that could have been used.

I think it may be ok if the ground and neutral go to the same circuit.
 
Last edited:

adsforpay

New Member
Messages
8
Reaction score
0
Points
0
Location
Arkansas
This is not really related to the original question... but I couldn't help but notice... On the top row of breakers, on the left is a 30A two pole labeled "Dryer", with what looks like 10Ga wire. Which is fine, but using those wires as a size comparison, on the right end of that same row of breakers is a 40A double pole, labeled "Air Cond", with what looks to be 12Ga wire. They look like the same size wire as on all the 15A and 20A breakers. If so, those wires are not protected by a 40A breaker. Maybe the OP can confirm or deny what seems to be in the pic.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
This is not really related to the original question... but I couldn't help but notice... On the top row of breakers, on the left is a 30A two pole labeled "Dryer", with what looks like 10Ga wire. Which is fine, but using those wires as a size comparison, on the right end of that same row of breakers is a 40A double pole, labeled "Air Cond", with what looks to be 12Ga wire. They look like the same size wire as on all the 15A and 20A breakers. If so, those wires are not protected by a 40A breaker. Maybe the OP can confirm or deny what seems to be in the pic.


The OP was asking about the grounds.

You are correct "This is not really related to the original question... "


But it is nice to keep people safe.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
That looks like the service panel or I would be more correct if I stated this looks like the service disconnecting enclosure and if my assumption is correct and the two terminal bars are bonded together and to the enclosure there is no problem with the panel.
What I said .
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
This is not really related to the original question... but I couldn't help but notice... On the top row of breakers, on the left is a 30A two pole labeled "Dryer", with what looks like 10Ga wire. Which is fine, but using those wires as a size comparison, on the right end of that same row of breakers is a 40A double pole, labeled "Air Cond", with what looks to be 12Ga wire. They look like the same size wire as on all the 15A and 20A breakers. If so, those wires are not protected by a 40A breaker. Maybe the OP can confirm or deny what seems to be in the pic.

We size the conductor by the minimum circuit amperage and the breaker by the maximum circuit amperage therefore it is possible to have #14 protected by a 40 amp breaker on any motor appliance such as AC or heat pump. The running overload that is in the compressor will protect the motor and conductors from overload. The breaker protects against ground fault and short circuits.
 