Hi all — hoping for ideas from anyone who has seen this specific flush issue on Navien tankless.
System: Two Navien NPE-240 units (one NPE-A2 and one NPE-S2) installed back-to-back on a rack and configured as a digital cascade (NaviLink). Each unit has its own hot/cold isolation valves and service ports. Units heat and supply domestic hot water normally.
Goal: Annual descaling/flush on one unit at a time (cascade keeps the house running).
The problem: On one unit, I cannot get flow out of the hot (red) service port during flushing — essentially zero flow / a tiny trickle.
System: Two Navien NPE-240 units (one NPE-A2 and one NPE-S2) installed back-to-back on a rack and configured as a digital cascade (NaviLink). Each unit has its own hot/cold isolation valves and service ports. Units heat and supply domestic hot water normally.
Goal: Annual descaling/flush on one unit at a time (cascade keeps the house running).
The problem: On one unit, I cannot get flow out of the hot (red) service port during flushing — essentially zero flow / a tiny trickle.
- I verified the valve handle turns and the ball valve visibly opens/closes (I’ll attach close-up pics of open/closed). The valve looks clean and unobstructed.
- The unit otherwise heats water normally at fixtures.
- Standard flush setup (per Navien style):
- Big cold/hot isolation valves closed
- Blue service valve open, red service valve open
- Pump into cold service, return from hot service into bucket
Result: pump can’t circulate; only drips/trickle at hot service port.
- House pressure test:
- Big cold isolation OPEN (city water feeding unit)
- Big hot isolation CLOSED (prevent sending anything to house)
- Blue service CLOSED
- Red service OPEN
Result: still only a tiny trickle out the hot service port even with hose removed.
- Verified cold side works:
- With house pressure I can get strong flow out the cold (blue) service port.
- Cleaned the Navien cold inlet filter screen — it was basically clean.
- Tried reverse-flow pump test (pump into hot service, return out cold service) — also no circulation.
- the hot service port is on the wrong side of the isolation/check arrangement, or
- there is an internal restriction in the service valve body/path that isn’t visible looking straight at the ball.
- Has anyone seen a Navien (or common tankless valve kit) where the hot service port has essentially no flow even though the ball opens?
- Is there a known check valve/backflow arrangement in some installs that can make the hot service port effectively “dead” for flushing?
- Any recommended diagnostic steps to confirm whether the hot service port is on the heater side vs house side of the isolation/check?
- If it’s a valve/port issue, is the right fix to replace the hot-side service valve assembly/kit?