While tidying up in my basement, I noticed some of the plastic plugs on top of my natural gas water heater showed signs of heat deformation. This problem seems to have appeared since we spent time on air sealing, insulating, and making other energy efficiency changes.

IMG_3944.JPG


Looking around, I discovered our house (built in 1929) does not have a make-up air inlet. I plan to remedy this shortly.

The water heater's exhaust passes through a couple of bends and finds its way into the lined chimney. Beyond adding the make-up air vent, is there anything I should change with the flue pipe on this installation? It appears the water heater was, at one time, electric and that this unit was a replacement some time ago.

Thanks again,

Nate

IMG_3945.JPG
IMG_3946.JPG
 

John Gayewski

In the Trades
Messages
4,348
Reaction score
1,342
Points
113
Location
Iowa
If you could get the run shorter by moving the heater or perhaps take one of the bends out of it and have it run straight into the chimney that is about all you can do to the vent to make it better.

It appears you have a large enough space are you sure you need an inlet.
 

Mke_Nate

New Member
Messages
5
Reaction score
0
Points
1
Location
Milwaukee, WI
If you could get the run shorter by moving the heater or perhaps take one of the bends out of it and have it run straight into the chimney that is about all you can do to the vent to make it better.

It appears you have a large enough space are you sure you need an inlet.
Thanks John, that is helpful advice. I'll try first to straighten out the run and shorten to the extent that I can.
 

Reach4

Well-Known Member
Messages
38,862
Reaction score
4,430
Points
113
Location
IL
I would lay a piece of steel over that plug to spread the heat out.
 

Tuttles Revenge

In the Trades
Messages
4,183
Reaction score
1,443
Points
113
We had a similar event at a clients. Turned out that the aluminum chimney liner had oxidized so much that the aluminum oxide dust had completely plugged the liner at the base where it turned out of the chimney.
 