Natural Gas Regulator Advice Needed

Users who are viewing this thread

two

New Member
Messages
1
Reaction score
0
Points
0
Location
36117
New to forum. Help please.

Have wood burning fireplace converted to gas logs with regulator (Maxitrol R400S) between gas meter and fireplce gas on/orr valve. Gas input to regulator is 2psig.

R400S regulator failed and was replaced with Maxitrol 325-3L. Prior to replacement, fireplace worked fine. Now have smell of burning plastic.

Research indicates that gas log fireplaces require 3.5-7" Water Column which the R400S provided, but the new 325-3L provides 7-11"" WC which may be providing incomplete combustion.

I want to install a 3-6/7" WC regulator but am told they are not available for a 2psi input, only for 1/2psi input.

So some questions:
1. Is 7-11" WC too high for a log fireplace?
2. Is there a 2psi input regulator will provide 3-6" WC?
3. If no such regulator, what can be done to get to 3-6" WC?

Thanks in advance.
 

John Gayewski

In the Trades
Messages
5,164
Reaction score
1,685
Points
113
Location
Iowa
Have you tried adjusting your regulator down? Most times they can be adjusted lower. Or usually you can buy a different spring for your existing regulator and it will adjust down.
 

Breplum

Licensed plumbing contractor
Messages
2,661
Reaction score
1,150
Points
113
Location
San Francisco Bay Area
Our regulator suppliers usually can help us find and build the right regulator. that is the best way to go.
but:
1. Is 7-11" WC too high for a log fireplace? Yes, likely, usually mfrs include regulator that takes it down to 3-6" WC (readily available)
2. Is there a 2psi input regulator will provide 3-6" WC? See my top line comment.
3. If no such regulator, what can be done to get to 3-6" WC? We NEVER want 2" PSI in a dwelling, too dangerous if there is a fire. We (UPC etc) want 7-11" WC running inside a house, then a small regulator at the appliance (same with most cooktops).
 

Bgard

Active Member
Messages
124
Reaction score
29
Points
28
Location
NW Indiana
The 325-5 regulator is designed for 2-5 PSI inlet pressure, if you’re house is only supplied with 7 IWC /1/4PSI the 325-series of regulators will not operate properly, the R400s is designed for 1/4 1/2 PSI / 7- 14 IWC , why did you replace the R400 with the 325 series? The R 400s is designed for precise pressure control at low volumes of flow
 