Meter Box Attached To Metal Pole Barn Siding

Users who are viewing this thread

ricpad

New Member
Messages
1
Reaction score
0
Points
1
Location
New York
Just wondering how grounding, bonding and separation of ground and neutral apply to a situation like this: A 200 AMP service meter box is attached to the metal siding of a pole barn using unistrut channels and the neutral in the meter box is bonded to the meter box which in turn bonds it to the metal siding via the unistrut channel. The main 200 amp panel has the Ground and Neutral buses bonded and the grounding electrode conductor originates here and terminates in two grounding electrodes. Does the neutral from the service being bonded to the metal pole barn siding pose a potential problem?
 
Last edited:

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
This is a common problem that is usually ignored. The siding (and more often metal conduit) will be a parallel path for the neutral current between the meter and main disconnect.
 