MegOhmMeter

Users who are viewing this thread

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
What's a good brand that's worth the extra money or a brand that's cheaper but still gets the job done.

Franklin said that we finally need to upgrade meters on their VFD's, over 50yrs and never needed one until today.

Franklin recommend a Uei Dmeg3
 
Last edited:

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
Megger is the big classic brand. I see Amprobe offers several, and that is a brand you know.

The older ones had an analog meter and a crank. Those were reliable. I see there are really cheap ones with an analog meter and a crank, but I don't know if they are any good.
 

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
Thank you Reach4.

I thought this would be a good read from Franklin Aid (12-1983)&(1-1984)
 

Attachments

  • WP_20160620_16_17_08_Pro.jpg
    WP_20160620_16_17_08_Pro.jpg
    85.9 KB · Views: 143
  • WP_20160620_16_18_15_Pro.jpg
    WP_20160620_16_18_15_Pro.jpg
    55.1 KB · Views: 139
  • WP_20160620_16_19_01_Pro.jpg
    WP_20160620_16_19_01_Pro.jpg
    77.9 KB · Views: 143
  • WP_20160620_16_19_43_Pro.jpg
    WP_20160620_16_19_43_Pro.jpg
    44.2 KB · Views: 134

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
More reading material from (2-1984)&(3-1984)
 

Attachments

  • WP_20160620_16_21_55_Pro.jpg
    WP_20160620_16_21_55_Pro.jpg
    84 KB · Views: 135
  • WP_20160620_16_22_34_Pro.jpg
    WP_20160620_16_22_34_Pro.jpg
    60.5 KB · Views: 116
  • WP_20160620_16_24_31_Pro.jpg
    WP_20160620_16_24_31_Pro.jpg
    74.4 KB · Views: 133
  • WP_20160620_16_25_05_Pro.jpg
    WP_20160620_16_25_05_Pro.jpg
    62.4 KB · Views: 126

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
Now to July/August 1990 "Tools of the Trade". Then Franklin came out with a 3 part on this topic.
 

Attachments

  • WP_20160620_16_29_41_Pro.jpg
    WP_20160620_16_29_41_Pro.jpg
    82 KB · Views: 130
  • WP_20160620_16_31_24_Pro.jpg
    WP_20160620_16_31_24_Pro.jpg
    79.2 KB · Views: 143
  • WP_20160620_16_33_49_Pro.jpg
    WP_20160620_16_33_49_Pro.jpg
    85.3 KB · Views: 125
  • WP_20160620_16_34_24_Pro.jpg
    WP_20160620_16_34_24_Pro.jpg
    57.3 KB · Views: 116
  • WP_20160620_16_36_01_Pro.jpg
    WP_20160620_16_36_01_Pro.jpg
    82.5 KB · Views: 126
  • WP_20160620_16_37_24_Pro.jpg
    WP_20160620_16_37_24_Pro.jpg
    98.9 KB · Views: 122

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
Part 3. "Tools of the trade: Insulation Resistsnce" & "Tools of the trade: Winding Resistance with more on my next post
 

Attachments

  • WP_20160620_16_39_03_Pro.jpg
    WP_20160620_16_39_03_Pro.jpg
    79.8 KB · Views: 130
  • WP_20160620_16_44_03_Pro.jpg
    WP_20160620_16_44_03_Pro.jpg
    90.3 KB · Views: 133
  • WP_20160620_16_44_33_Pro.jpg
    WP_20160620_16_44_33_Pro.jpg
    77.8 KB · Views: 142
  • WP_20160620_16_45_06_Pro.jpg
    WP_20160620_16_45_06_Pro.jpg
    69.1 KB · Views: 116
  • WP_20160620_16_45_36_Pro.jpg
    WP_20160620_16_45_36_Pro.jpg
    87.3 KB · Views: 154
  • WP_20160620_16_48_11_Pro.jpg
    WP_20160620_16_48_11_Pro.jpg
    76.4 KB · Views: 124

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
The rest of Windings Resistance
 

Attachments

  • WP_20160620_16_49_46_Pro.jpg
    WP_20160620_16_49_46_Pro.jpg
    92.3 KB · Views: 138
  • WP_20160620_16_50_45_Pro.jpg
    WP_20160620_16_50_45_Pro.jpg
    70 KB · Views: 130

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
What's a good brand that's worth the extra money or a brand that's cheaper but still gets the job done.

Franklin said that we finally need to upgrade meters on their VFD's, over 50yrs and never needed one until today.

Franklin recommend a Uei Dmeg3

That is because with a VFD on a 230 volt system you will get running voltage spikes of up to 1000 volts. And since the wire insulation and everything else is only rated to 600 volts, it is important to use a meg ohmmeter to check for a short. The old Simpson at Rx100K is not sensitive enough. So yes if you throw the VFD away you won't need a meg ohmmeter.

And the analog meters are not good enough because the young techs don't know how to read one. You have to give them a number off a digital meter that they can match up with a number in their cheat sheet manual to be able to help you.

But I do use them for deep set and high voltage applications. This is the one I use. I think it is dated about 1950.

20160620_155507_resized.jpg
 

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
That is because with a VFD on a 230 volt system you will get running voltage spikes of up to 1000 volts. And since the wire insulation and everything else is only rated to 600 volts, it is important to use a meg ohmmeter to check for a short. The old Simpson at Rx100K is not sensitive enough. So yes if you throw the VFD away you won't need a meg ohmmeter.

And the analog meters are not good enough because the young techs don't know how to read one. You have to give them a number off a digital meter that they can match up with a number in their cheat sheet manual to be able to help you.

But I do use them for deep set and high voltage applications. This is the one I use. I think it is dated about 1950.

View attachment 34821

Thanks for showing us your old meter that still works
 

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
IF, you throw the VFD in the trash where they belong, you don't need a megger

This replaced a CSV system (2 different brands of pump ends, not thrust bearings) that we discussed on here before when I first joined this forum and how I was concerned about the Franklin SD control box being waterproof. It got a short circuit fault code over the weekend and I wanted to find out why and this is when Franklin wanted a megometer to check the wires before Franklin says it's the control box, slice or motor.

Took the customer to his long lasting traditional system again (it's about 200' away from this one where he knows how much it cycles), and now he sees why we recommend old school traditional systems.
 
Last edited:

Boycedrilling

In the Trades
Messages
837
Reaction score
185
Points
43
Location
Royal City, WA
I've got two both 20 plus years old. A Bidgle that I bought used on eBay for about $250, 20 or more years ago. My other one, which I used daily is a mi,Italy surplus unit. I bought 10 of them brand new, surplus in the mid 90's for $75 each. Sold the other 9 for $150 each and kept one for myself. Haven't used it since yesterday.
 

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
I've got two both 20 plus years old. A Bidgle that I bought used on eBay for about $250, 20 or more years ago. My other one, which I used daily is a mi,Italy surplus unit. I bought 10 of them brand new, surplus in the mid 90's for $75 each. Sold the other 9 for $150 each and kept one for myself. Haven't used it since yesterday.

Thank You for sharing
 

ThirdGenPump

In the Trades
Messages
184
Reaction score
29
Points
28
Location
MA
I prefer my old Simpsons. It's never come up that they might be insufficient. I can see how it's an issue on the top end. I have a high end Fluke meters I can go to if I needed, when I was working as an electrician they were worth having. I don't see much reason in carrying around 500 dollar meters for regular business. Don't want to risk banging them up. I like analog meters, the Fluke ohm meter is digital.

My meters are in my service bag so can get beat up. Greenlee multi meter, that's used soley as an amp probe, I'll use it for ohms or voltage if I want a second opinion. Simpson Ohm Meter. Knopps voltage tester.
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
The deal is that a regular voltmeter puts less than 10 volts between the things you are looking for a point of breakdown. With a meter that puts 500 to 1000 volts across the pieces being checked, a problem can be detected that might not have shown up at a low voltage.

https://terrylove.com/forums/index.php?threads/new-submersible-pump-not-working.65039/#post-490018 is a recent posting where a regular ohmmeter did not detect the problem, but the high voltage megohmeter probably would have.
 

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
I prefer my old Simpsons. It's never come up that they might be insufficient. I can see how it's an issue on the top end. I have a high end Fluke meters I can go to if I needed, when I was working as an electrician they were worth having. I don't see much reason in carrying around 500 dollar meters for regular business. Don't want to risk banging them up. I like analog meters, the Fluke ohm meter is digital.

My meters are in my service bag so can get beat up. Greenlee multi meter, that's used soley as an amp probe, I'll use it for ohms or voltage if I want a second opinion. Simpson Ohm Meter. Knopps voltage tester.

Thank you for sharing
 

ThirdGenPump

In the Trades
Messages
184
Reaction score
29
Points
28
Location
MA
The deal is that a regular voltmeter puts less than 10 volts between the things you are looking for a point of breakdown. With a meter that puts 500 to 1000 volts across the pieces being checked, a problem can be detected that might not have shown up at a low voltage.

https://terrylove.com/forums/index.php?threads/new-submersible-pump-not-working.65039/#post-490018 is a recent posting where a regular ohmmeter did not detect the problem, but the high voltage megohmeter probably would have.

Yeah I get it, the Fluke I have can put out 1000v. If I was having trouble with a VFD I might consider grabbing it to double check. As it is now I've never come across a situation where I've needed to doubt the Simpson in well work.

On the electrical side we wanted to be really sure if a 2000 amp service wasn't going to explode when we put power to it.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
This replaced a CSV system (2 different brands of pump ends, not thrust bearings)

What pumps did you have and how deep was it to water? My guess is the pressure switch was set too close to the deadhead of the pump, and you were not getting the 1 GPM needed to keep the pump cool. Or it could have just been bad pumps. Failures with a CSV are nearly always installer error, not the function of the CSV.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
The deal is that a regular voltmeter puts less than 10 volts between the things you are looking for a point of breakdown. With a meter that puts 500 to 1000 volts across the pieces being checked, a problem can be detected that might not have shown up at a low voltage.

https://terrylove.com/forums/index.php?threads/new-submersible-pump-not-working.65039/#post-490018 is a recent posting where a regular ohmmeter did not detect the problem, but the high voltage megohmeter probably would have.

Yeah that 1000 volts simulates the spikes from a VFD. That way you can see if there is any little defect in the 600 volt wire insulation that would cause a ground fault when connected to a VFD. But a 480V VFD system has spikes of up to 2000 volts, so sometimes even a megger isn't sensitive enough to pick up a problem.
 

PumpMd

Kevin
Messages
567
Reaction score
42
Points
28
Location
Oklahoma
Well specs: (I forgot to mark the depth to water in the file but I checked it for you on the last pump removal) 70' to H2O is our average, Pump set at 200' on 1 1/4 sch80.

All of this was gone over on my thread called "Our CSV Systems", my user name was "Letsrunum" and you can't find it now. You said "maybe it's to big of a pump on the small tank" after going over everything. I believe it was your 70psi brass CSV, since it had a heavy duty switch to shutoff at 75psi.

7-2007 through 8-24-15
1 1/2hp Pentek with S/S Pro-Source pump 16gpm (tried Twice)
1 1/2hp Franklin with Water Horse pump 15gpm (tried Twice)

Installed the first pump in 07, warranted that in 2009, again in 2010, then once more in 2012. Jacuzzi design was used since it was before 2015.
 