Hi,
My two main questions are:
1. Which of the Appendix A 105.1 charts would I use for PEX pipe?
2. Do the below calculations seem correct?
I'm in Seattle where the city uses the UPC with some local changes (2021 Seattle Plumbing Code) and, for a large 2-unit residential remodel construction project, I'm trying to use Appendix A to calculate if my current 3/4" meter will be sufficient. Unfortunately, I can't easily upsize the meter without first installing a new water main for the street which would involve redoing a large section of the right of way at a high cost (which I'm hoping to avoid).
The stock sizing table 610.4 only includes up to 1-1/4" building supply lines for a 3/4" meter (I might need to do a bigger supply) and also is a rougher estimate with just 3 groups of pressure values. Given I'm likely going to be pushing the limits here, I'm trying to use the alternate approach from Appendix A to calculate more precisely.
Relevant info & calculations
Overall, I'm hoping to be able to provide supply for 68.5 water fixture supply units, from table A 103.1:
Clothes washer: 2 x 4 =8
Toilet: 10 x 2.5 = 25
Lav: 10 x 1 = 10
Shower: 8 x 2 = 16
Kitchen Sink: 2 x 1.5 = 3
Dishwasher: 2 x 1.5 = 3
Hose bib: 2.5 + 1 = 3.5
First I found the demand in GPM for the 68.5 units:
Then:
A 102.2 Water Meter
I'm not sure if I have a disk jet water meter or a multi-jet one (or some other kind) but using the disk meter chart (chart A 102.2) I noted 25 psi loss at 35GPM
A 104.1 Residual Pressure
Using 8 psi for flush tank
A 104.2 Elevation
Elevation difference is 33' so 33 * 0.43 = 14.19
A 104.2 Available Pressure
68psi (value provided by the water company for static pressure at meter) - 25psi (from meter) - 8psi (for highest fixture) - 14.19psi (from elevation) = 20.81psi
A 104.4 Developed Length
100' total so 20.81psi/100'*100 = 20.81 as the average permissible loss per 100'
For copper, per 610.12 the max allowed velocity is 8ft/sec so I believe I would need a 1-1/2" main supply:
Thanks!
My two main questions are:
1. Which of the Appendix A 105.1 charts would I use for PEX pipe?
2. Do the below calculations seem correct?
I'm in Seattle where the city uses the UPC with some local changes (2021 Seattle Plumbing Code) and, for a large 2-unit residential remodel construction project, I'm trying to use Appendix A to calculate if my current 3/4" meter will be sufficient. Unfortunately, I can't easily upsize the meter without first installing a new water main for the street which would involve redoing a large section of the right of way at a high cost (which I'm hoping to avoid).
The stock sizing table 610.4 only includes up to 1-1/4" building supply lines for a 3/4" meter (I might need to do a bigger supply) and also is a rougher estimate with just 3 groups of pressure values. Given I'm likely going to be pushing the limits here, I'm trying to use the alternate approach from Appendix A to calculate more precisely.
Relevant info & calculations
Overall, I'm hoping to be able to provide supply for 68.5 water fixture supply units, from table A 103.1:
Clothes washer: 2 x 4 =8
Toilet: 10 x 2.5 = 25
Lav: 10 x 1 = 10
Shower: 8 x 2 = 16
Kitchen Sink: 2 x 1.5 = 3
Dishwasher: 2 x 1.5 = 3
Hose bib: 2.5 + 1 = 3.5
First I found the demand in GPM for the 68.5 units:
Then:
A 102.2 Water Meter
I'm not sure if I have a disk jet water meter or a multi-jet one (or some other kind) but using the disk meter chart (chart A 102.2) I noted 25 psi loss at 35GPM
A 104.1 Residual Pressure
Using 8 psi for flush tank
A 104.2 Elevation
Elevation difference is 33' so 33 * 0.43 = 14.19
A 104.2 Available Pressure
68psi (value provided by the water company for static pressure at meter) - 25psi (from meter) - 8psi (for highest fixture) - 14.19psi (from elevation) = 20.81psi
A 104.4 Developed Length
100' total so 20.81psi/100'*100 = 20.81 as the average permissible loss per 100'
For copper, per 610.12 the max allowed velocity is 8ft/sec so I believe I would need a 1-1/2" main supply:
Thanks!