Over the last several months, we have noticed water pressure dropping while showering. Further investigation shows the pressure drop to be throughout the house and isolated to the hot water circuit.
Attaching a pressure gauge to the municipal water supply, after the inline pressure regulator, shows about 58psi, and drops to around 53psi when any kind of water use happens, hot or cold. This seems normal.
Same pressure gauge when attached to the hot water return line (we have a circulator), shows 58psi and drops to around 10psi when two or more hot water sources are used (shower and kitchen sink for example).
There is no easy way to tap into the cold water supply to the water heater or the outlet of the water heater. Test was done while circulator pump was running, so that was not a restriction.
The water heater is an indirect design, and is about 16 years old. It is a Weil-Mclain brand and should be stainless steel and good for 25-30 years.
Our water is just slightly hard, and there is no evidence of scaling or build up anywhere in the house (I even cracked open one of the flow check valves on the cold water supply and it was clean as a whistle).
I have noticed that there is a corrosion build up on the inlet and outlet unions of the water heater. I am not familiar with these types of unions, and thus not comfortable cracking them open to see how extensive the corrosion may be internally. Photo attached.
I am kind of at a loss where this restriction may be living on the hot water circuit and looking for suggestions.
Thanks,
Todd
Attaching a pressure gauge to the municipal water supply, after the inline pressure regulator, shows about 58psi, and drops to around 53psi when any kind of water use happens, hot or cold. This seems normal.
Same pressure gauge when attached to the hot water return line (we have a circulator), shows 58psi and drops to around 10psi when two or more hot water sources are used (shower and kitchen sink for example).
There is no easy way to tap into the cold water supply to the water heater or the outlet of the water heater. Test was done while circulator pump was running, so that was not a restriction.
The water heater is an indirect design, and is about 16 years old. It is a Weil-Mclain brand and should be stainless steel and good for 25-30 years.
Our water is just slightly hard, and there is no evidence of scaling or build up anywhere in the house (I even cracked open one of the flow check valves on the cold water supply and it was clean as a whistle).
I have noticed that there is a corrosion build up on the inlet and outlet unions of the water heater. I am not familiar with these types of unions, and thus not comfortable cracking them open to see how extensive the corrosion may be internally. Photo attached.
I am kind of at a loss where this restriction may be living on the hot water circuit and looking for suggestions.
Thanks,
Todd