Hi guys,

I am looking to vent a kitchen sink that doesn't have easy access to the existing vent system. I understand diagram B in the attached image is code for a loop vent as they are typically used in kitchen island where the loop is directly below the counter. In my situation the loop vent would be in a wall and could go above the sink's flood elevation. My question is would the system in diagram A be acceptable as the loop is above the flood elevation at the sink but the actual vent connection to existing main stack is below in the basement?
 

Attachments

  • Capture - Copy.JPG
    Capture - Copy.JPG
    36.5 KB · Views: 269

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
Other than the issue Terry cited, either A or B would be fine for a loop vent. The connection from vent to drain occurs at the low point of the vent; after that point, the vent just has to follow the usual vent rules (other than the height of the horizontal segment), so it can rise up before hitting the main stack.

But the main question is whether you can get approval for a loop vent for a sink that isn't on an island. Lack of easy access may not be sufficient justification for the loop vent; you may have to just do it the normal, hard way.

Cheers, Wayne
 

Richard978

New Member
Messages
2
Reaction score
0
Points
1
Location
Boston
Good catch. Yes, the wye would go in the flow direction. Opposite of what I drew. Thank you!
 