Terry, Thanks for the quick response. It sounds like it has to be either the loop or the AAV or raise the horizontal vent to meet the code requirement. I'll look to redesign. Now as an intellectual exercise, purely from a functional point of view, why is long trap arm (42" for 1 1/2" and 60" for 2") better than horizontal dry vent? Wouldn't the long trap arm be more likely to plug requiring more frequent clean out. The horizontal vent would only fail and require cleanout after an overflow event?
Also wouldn't my two options perform better than the loop vent and the AAV?
Normal condition: sink does not overflow
Option 1: No issues
Option 2: No issues
42" height horizontal vent: No issues
Loop Vent: No issues
AAV: could fail over time as it has moving parts and seals, etc.
sink backs up and overflows:
Option 1: liquid backs up to the horizontal section, possible accumulation of solids, potential plugging and loss of vent function, require snaking of the vent to mitigate.
Option 2: liquid backs up to the horizontal section, possible accumulation of solids, potential plugging and loss of vent function, might be better than Option 1 since the slope is bigger, require snaking of the vent to mitigate
42" height horizontal vent: No issues as the sink will overflow and no liquid will travel to the horizontal section
Loop Vent: if drain stop is further downstream of the loop then the liquid will fill the vent line including the horizontal sections, possible accumulation of solids and potential plugging and loss of vent. require snaking through cleanout. As the horizontal vent line is lower with minimal slope, accumulation could be worse than Options 1 & 2?
AAV: more opportunity for failure if valve does not properly seat.