Is this wet vented bathroom done correctly?

SamTG

New Member
Messages
1
Reaction score
1
Points
1
Location
Canada
Hi everyone,

I was hoping to get some feedback on this 2nd floor wet vented bathroom diagram.

Any thoughts?

thanks in advance,
 

Attachments

  • Plumbing_WC_SA.png
    Plumbing_WC_SA.png
    77.9 KB · Views: 64

John Gayewski

In the Trades
Messages
5,215
Reaction score
1,705
Points
113
Location
Iowa
It's fine for a wet vent in some states. If your going to be that close to 8 feet on a 2" trap arm you have to make sure your slope is correct. Overslope and your not vented, underslope amd you get bad drainage.

Amd chat gpt doesn't know anything about plumbing. Ask it the same question over and over again differentl and you get differnt answers. Ask it specific questions about where and when and why it came up with an answer and it'll give you the wrong answer but insist it's right even though it's showing you that it's wrong. AI is a very good internet seach tool that grabs things it found in common. It can't actually think.
 

Jeff H Young

In the Trades
Messages
9,906
Reaction score
2,518
Points
113
Location
92346
Looks good and the precautions of having just the right amount of fall basically not to exceed 2 inches but in your case of 7ft 6 inches you need to have not less than 1 7/8 inches . Im going to just call it exactly 1/4 inch perft . My code only allows a 5 ft run but yours allows 8 ft
 