Is this wet vent a UPC violation?

Users who are viewing this thread

Olmedo

New Member
Messages
5
Reaction score
0
Points
1
Location
Point Roberts, WA
Quick check here please?
 

Attachments

  • Plumbing.png
    Plumbing.png
    95.8 KB · Views: 373

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
The trap arms can have 1/4" per foot grade up to 42" long. The moment you turn them up with 90 degree bends it doesn't work.

double_lav_rough_1.jpg


Trap arms like this, and 2" all the way up including the vent. This one wasn't a wet vent so the vent was only 1.5".
 

Olmedo

New Member
Messages
5
Reaction score
0
Points
1
Location
Point Roberts, WA
The trap arms can have 1/4" per foot grade up to 42" long. The moment you turn them up with 90 degree bends it doesn't work.

double_lav_rough_1.jpg


Trap arms like this, and 2" all the way up including the vent. This one wasn't a wet vent so the vent was only 1.5".

I was actually talking about the vent for the water closet but very glad you told me about the lav traps as well. I actually don't know why I had them turned like that in the pic because the cross is already at 19" so no need for that. How about the WC?
 