If you run the shower into the stack separately and connect it with a san-tee, the stack can be the shower vent if the only fixtures draining into the stack above that san-tee are other bathroom fixtures from the same floor level. Otherwise, you need a different strategy for venting the shower.
If draining through that combo were only bathroom fixtures from at most 2 bathrooms on the same floor, then the combo connection could serve as a horizontal wet vent, and the shower would be vented. But because you have a kitchen sink and a bathroom upstairs running through there, your pictured layout would not have a vent for the shower.
One option would be to dry vent the shower; if the stack you are connecting to has no drainage from the floor above (and goes up through the roof), you could connect the vent to the stack above all the drains and at least 6" above the shower flood level. If it has drainage from the floor above, you'd have to run the vent separately to a height where you can connect above all the drains. Or else use an AAV in a wall enclosure (since MD uses the IPC, if I recall).
Another option is to wet vent the shower by splitting the horizontal 2" drain going up and down the page on your photo. One branch would carry the kitchen sink and any upstairs fixtures (all of which should already have been vented). The other would carry the sink in the same bathroom (which will need a dry vent, either atmospheric or an AAV), plus possibly other bathroom fixtures, and then pick up the shower. That allows the sink in that bathroom to wet vent the shower; after the shower comes in, the two separate horizontal drains (local bathroom group and more distant drains) could combine before joining the stack.
Cheers, Wayne