Is this plumbed incorrectly?

Users who are viewing this thread

seann

In the Trades
Messages
45
Reaction score
2
Points
8
Location
Nebraska
Stupid question probably but is this plumbed incorrectly? I was told it is breaking the vent to the toilet and the shower, but it seems like it should functionally be fine. What am I missing? Double 45 to toilet, and double 45 to shower drain in the photos. The 2" wye is tied to a 2"vent on the wye side. The double 3" 45s are going up to a toilet.

7152.jpeg
7155.jpeg
7154.jpeg
7153.jpeg
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
The trap arm can only rise at a 2% slope. That would be 1/4" per foot and max out at eight feet on some codes, five on others.
The moment you 45 or 22 up you've created an S trap which siphons. Toilets siphon anyway, so they have some different rules on their venting.
 