Iron won't settle in chlorinator tank

Users who are viewing this thread

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
I've got a deep drilled well that produces really disgusting water. Smells bad, tastes bad, but passes health department tests. I suspect bacterial iron among other problems, but that theory was poo-pooed by a local well expert (appropriately named "Rusty").

It gets chlorinated via a Pulsafeeder pump just before going into a 125 gallon settling tank. However, the oxidized (I assume) iron remains suspended in solution. When I open the drain at the bottom of the tank, a brief shot of rusty water comes out, but then runs clear. About once a year I remove the tank and pressure-wash it, but I've never seen any sign of iron buildup.

The problem is, of course, that the suspended iron gets passed on to the carbon filter, resin tank, and house. I put in a couple of filters (one stainless steel mesh to get out the big pieces, one cheap spun filter) which help a lot, but we still see iron buildup over time on the bottom of the dish drainer and other places where small amounts of water accumulate and evaporate over time. Other than that, the resulting water doesn't smell, looks clear, seems OK, tastes good.

I asked Rusty if there was a better filter I could use, but he suggested I just add soda ash to the chlorine tank to adjust the pH. Didn't help. He doesn't seem anxious to take any of my money.

At this point I'm thinking of replacing the cheap spun filter with one of the big blue jobs, but would welcome any suggestions.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
For reasons that I won't try to explain here unless asked, the effectiveness of a settling tank is related to the plan-view area of the tank and the settling velocity of the particles. Since iron particles are small unless coagulated, they settle slowly. A round tank that is 4 diameters long is 5 times as effective as a settling tank if it is laying on its side as it is if it is upright.

Your settling tank is probably useful as a retention tank to let the oxidation process take place, but probably not as a settling tank. That is confirmed by your experience.

Where you are getting lots of colloidal iron, I would try inexpensive cotton string-wound filters. Cotton tends to expand when wet and becomes more effective with use. I use the tightest wound cotton filters that I can get to meet requirements for removing giardia, and they hold a lot of dirt before getting plugged.

The pleated 1-micron cartridges that I use in the Big Blue housings do a great job of removing crypto and that sort of stuff but are more expensive than necessary for removing iron particles and don't have as long a life on a gallons per dollar basis for removing ordinary suspended material.

What kind/how big/how many housings do you now have? You could probably try the cotton filters.
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
A backwashable iron filter is what you need. That should have been the first unit after the retention tank. Instead, you are gumming up your carbon. I hope that carbon filter has a backwashable head. The iron that gets through the carbon will also help gum up the resin in your softener.

bob...
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
My tank is about 6' tall and maybe 18" diameter -- roughly the 4x tank you mentioned. There's a 200-mesh Rusco spin-down filter at the outlet, followed by a 10" filter which currently has a cotton-wound element in it; they seem to last about 60 days. Our average usage is 125.5 gpd, which includes water used for backwashing.

The carbon filter is backwashable. It's a fiberglass tank about 5' tall, 10" in diameter, same as the softener resin tank. I'm pretty sure the heads are Fleck, but there's absolutely no manufacturer's identification on them. I can post a picture tomorrow if necessary. I'm pretty sure it's set to backwash every 6 days. I had the carbon filter rebedded about 3 years ago, and at that time it seemed pretty filled up with iron. Softener resin has never been changed since installation, maybe 8? years. Probably time to rebed them both?

What kind of backwashable iron filter do you recommend?

The city (pop. 1700) is making annexation and water & sewer noises, so I don't want to spend huge bucks on this if we have to shut down the well soon. OTOH, we want good water, and a few hundred bucks more is a drop in the bucket (so to speak) in the grand scheme of things.

Whatever I do, I need an Idiot's Guide to Managing Your Water System. I have no clue how often these things should be backwashed, what the residual chlorine level and pH should be coming out of the settling tank, etc. Installer gave me a swimming pool test kit marked where he says things should be, but I have a hard time distinguishing the colors very well. Local extension office hasn't been much help, nor have local water guys, who all want to sell a new system.
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
If it were mine I might try to keep the chlorine at a very good minimum and change the media in the carbon filter to MTM or some other type of iron removal media. You can remove the chlorine in your drinking water with any carbon based filter at the sink.

Don't get me wrong, I really don't like injecting chlorine into anyone's house if it is possible to do something else, but the carbon can't be lasting long with all the iron it is accumulating.

You will probably still need the equipment with the proposed city water. They never take out hardness and you can be almost assurred there will be chlorine or some other bug killing agent in the water.

bob...
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
I don't mind the chlorine. We can't taste it or smell it in the house, and it gives us a good feeling about killing whatever can be killed with chlorine. After a major storm, most municipalities are under a boil-water order for several days, which doesn't affect us. What is a "very good minimum" chlorine level?

I had definitely planned on keeping the equipment after converting to city water -- could probably extend the backwash period for both tanks, since we're starting with (presumably) decent water.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Just about midway between Orlando and Tampa -- in the Polk City suburbs. Looks like maybe an hour or so from Riverview.
 
Last edited:

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Yeah, we were something like 18mi from the epicenter. It was kind of thrilling seeing 10' waves on our lake which is about 15' deep at its deepest. When I say "central Florida" we're actually about 60 miles from the geographic center of Florida, which bears roughly northwest of us. Oddly enough, the geographic center is closer to the coast than we are, thanks to the panhandle hanging out there. Even more oddly, I just noticed that every Web site which gives both geographic description of the geographic center (12 mi. NNW of Brooksville) and Lat/Lon (28d8.0m N, 81d 37.9m W) have apparently not noticed these two points are about 65 miles apart.
 
Last edited:

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
I'm not too sure, but I think Scary may be a better term for those ten foot waves. I've been in a few of those out in Tampa bay in a 23 foot boat when one of those crazy Bay Pilots was in a hurry to return a large freighter to port.

I'de say where you are and Brooksville are kind of a fur piece apart.

bob...
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
It sounds as if you aren't injecting enough chlorine, and/or the solution is too weak. And if the pH is wrong for the use of chlorine, you won't get it working right. And you have to get the pH right before injecting the chlorine.

The retention tank may not be large enough but, does the outlet go out the top, as it has to?

A spin down 'filter' is not a good choice. Disposable cartridges aren't either. You could use Centaur carbon in your filter and replace the filters and retention tank with a special 12" x 60" mixing tank. And it's all within your few hundred dollars range.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Gary --

What's special about a "mixing" tank? Mine is a 125-gallon tank, and that's our average daily usage, so there's an average 24 hour contact time. It's about 6' tall by 18" in diameter; water enters about 6" from the bottom, exits at the top.

What's special about Centaur carbon? Isn't carbon carbon?

What values do you suggest for pH and residual chlorine? What test kit do you recommend?

I'm off to the QWA Web site for a while, I guess.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
An 18 inch diameter x 6 ft long tank is about 80 gallons, not counting losses in rounded head or the concave bottom. If someone sold you that as a 125, you were shorted about 45 gallons.
 

PEW

DIY Senior Member
Messages
484
Reaction score
0
Points
16
I went that route, gave up on it, and for the last 10 years have used a green sand filter with great success. But, our problem was only iron.

Paul
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Part of my problem is I don't know what my problem is. The water-treatment guy had done a bunch of neighbors' houses and they all thought he was great, so I just called him up and said go to it. He never tested the water, apparently because he figured everybody in the neighborhood was poking into the same formation, so we stood to have the same problems.

Checked on some things:

Well is 220 feet, cased to 160 feet

Tank is a model Q120V, from Quick Tanks Inc., Kendallville, IN. Very basic Web site, but they confirmed it's a 120 gallon tank. Actual measurement is consistent with that.

Still haven't made it to Gary's site, but I promise...
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
Getting back to the original idea of trying to fix your water. Why don't you send me a sample of your water. A pint will be plenty. I will need it before any of your equipment. Preferably at the well.

If you want to do this, PM me and I'll give you the address to mail the water to. At least we can see what you have in your water and why Rusty said to add soda ash. Sounds like you might have a low PH.

bob...
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
A few ideas/guesses... Since you are seeing rust stains past the equipment, you are not getting all the iron with the chlorine. IF you have IRB, you'd usually have an odor too, you aren't getting enough chlorine and the retention time is too short. So, dump your solution and mix another batch and then raise the amount of chlorine being dosed. Then test the water for chlorine after the chlorination, before the carbon or other filters for free chlorine; you need between .2 and 1.5 ppm.

Then run a resin cleaner through the softener. It may be loaded up with iron adding it to the water. Make sure the water is always soft past the softener. If not, you are overrunning the capacity or your leakage is more than acceptable.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Gary Slusser said:
A few ideas/guesses... Since you are seeing rust stains past the equipment, you are not getting all the iron with the chlorine.

My thoughts exactly.

IF you have IRB, you'd usually have an odor too, you aren't getting enough chlorine and the retention time is too short.

We used to get bad odor on the hot-water side. I replaced the water heater (I cut apart the old one; it was indescribably nasty) but the odor returned shortly. I replaced the magnesium anode rod with aluminum, and it's helped a lot, but I occasionally get a whiff of H2S-smell.

So, dump your solution and mix another batch and then raise the amount of chlorine being dosed. Then test the water for chlorine after the chlorination, before the carbon or other filters for free chlorine; you need between .2 and 1.5 ppm.

Seems to me I'm seeing around .5ppm as I remember. I can both increase the strength of the solution and raise the injection rate to get the residual up.

Then run a resin cleaner through the softener. It may be loaded up with iron adding it to the water. Make sure the water is always soft past the softener. If not, you are overrunning the capacity or your leakage is more than acceptable.

Resin cleaner? I've learned something new. Very possibly it's loaded up. How do I "run it through" the softener?

I use the blue-bag iron-removing salt in the brine tank, but when we rebedded the carbon filter 3 or 4 years ago it had a bunch of iron in it, so it's likely some has found its way into the softener tank. Water still seems soft -- I think I notice when it regenerates, though, so that may be an indication it's not working at peak performance. The resin is probably 8 years old.

No leaks -- guar-an-damn-teed. It wasn't easy getting there, though.
 
Last edited: