Clueless in Charlotte
New Member
I have recently starting having an intermittent issue with low voltage but only on one 120V leg. My house is 2 years old, on a slab and the incoming power lines are underground. The first time it happened my kitchen overhead lights went out during the day so I thought we had lost all power. However, I soon discovered it was just some circuits that were down. I called the power company and they said to turn the range (220V) on. As soon as I did that the lights came back on. I didn't check any voltages because I assumed it was just an anomaly.
The next weekend the kitchen lights (LED bulbs) starting flickering and dimming. This time I turned off the main breaker, removed the circuit breaker panel cover and checked voltage on both legs. One leg was good (~123V) but the other leg was only 65V and only 37V if I swapped the test leads. Hot to hot read only 159V and dropped to 132V with the test leads reversed. Please note that I was reading the voltage with the main breaker off. I assume that means that it could not possibly be a bad breaker or loose connection in the panel or house wiring. If that is an incorrect assumption please let me know.
The main breaker was off for about an hour and when I turned it back on I noticed the digital HVAC thermostat didn't come back on. While I was researching that my wife noticed it came back on and the air conditioner started running. After that the voltage was back to normal. Both incoming legs read 123V and I get ~240V across legs. Readings are the same with the test leads reversed.
The next night 2 breakers tripped so I had an electrician come out the following day. After telling him my findings he said to call the power company. Customer service at the power company was supposed to put in a request for a monitor on the meter.
The next weekend the lights and circuits on the suspect leg went out again. One leg was normal but the other leg was low voltage just like before. I called the power company and they said they would dispatch technicians. After 5 or 10 minutes the power in the suspect leg was back to normal. The technicians arrived about an hour later but they didn't really do anything except read the (now good) voltages. They said the guy who would put the monitor on was out until Monday.
The circuit breaker panel and the meter are on opposite sides of the same wall, less than 1 foot apart. Again, when the problem is present, 1 leg reads low voltage with the main breaker off so I assume there is a bad connection or splice between the transformer and the meter. However, the technicians said there could not be an issue with the connection at the transformer (hard to believe).
Does anyone has any ideas on what the problem could be or how I should proceed? The power company hasn't been very helpful and still hasn't put a monitor on the meter as far as I know.
The next weekend the kitchen lights (LED bulbs) starting flickering and dimming. This time I turned off the main breaker, removed the circuit breaker panel cover and checked voltage on both legs. One leg was good (~123V) but the other leg was only 65V and only 37V if I swapped the test leads. Hot to hot read only 159V and dropped to 132V with the test leads reversed. Please note that I was reading the voltage with the main breaker off. I assume that means that it could not possibly be a bad breaker or loose connection in the panel or house wiring. If that is an incorrect assumption please let me know.
The main breaker was off for about an hour and when I turned it back on I noticed the digital HVAC thermostat didn't come back on. While I was researching that my wife noticed it came back on and the air conditioner started running. After that the voltage was back to normal. Both incoming legs read 123V and I get ~240V across legs. Readings are the same with the test leads reversed.
The next night 2 breakers tripped so I had an electrician come out the following day. After telling him my findings he said to call the power company. Customer service at the power company was supposed to put in a request for a monitor on the meter.
The next weekend the lights and circuits on the suspect leg went out again. One leg was normal but the other leg was low voltage just like before. I called the power company and they said they would dispatch technicians. After 5 or 10 minutes the power in the suspect leg was back to normal. The technicians arrived about an hour later but they didn't really do anything except read the (now good) voltages. They said the guy who would put the monitor on was out until Monday.
The circuit breaker panel and the meter are on opposite sides of the same wall, less than 1 foot apart. Again, when the problem is present, 1 leg reads low voltage with the main breaker off so I assume there is a bad connection or splice between the transformer and the meter. However, the technicians said there could not be an issue with the connection at the transformer (hard to believe).
Does anyone has any ideas on what the problem could be or how I should proceed? The power company hasn't been very helpful and still hasn't put a monitor on the meter as far as I know.