A friend of mine is finishing his basement, and when the new house was built a year ago, he had a pre-wire for a sub panel down there. Anyway his main panel has 2, 50A breakers, and the wire is bugged off in the basement in a JB. i did not check the wire yet to make sure its #6 or #4 yet, but I was wondering if there is any issues with splicing off the JB and then goin to the new sub panel?
 

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
As long as the jbox is large enough, the devices you use are listed for the size of wire you have, and the jbox is accessible when you are finished, it's perfectly OK.
 

projectorguru

New Member
Messages
17
Reaction score
0
Points
0
Really? Here you can't have a junction on the feed to a sub-panel - it has to be a continuous run of wire.

That was my point, I thought code was it has to be continuous, but I couldn't find it anywhere. Also they used 2 50 amp breakers which i though was wrong as well
 

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
The NEC does not prohibit spicing feeders, so it must be a local amendment.
 