Heat loads and units were sized by local company. The boiler supplies two air handlers, a large basement of radiant heat, and one zone of baseboard.
Modulating unit, 105k btu.
The local company may or may not have competently calculated the heat loads . Unless this is a very large (5000'+ ) or very leaky (little to no insulation, antique single pane windows), my suspicion is that it was not done correctly. A 105KBTU/hr boiler is ridiculously oversized for almost all houses in the US, but may have been sized for the (also oversized) air handlers.
The minimum modulated output is more important than the max. Without the model number I can't look it up, but what is the MINIMUM BTU-input (or output) of that boiler?
When it comes to serving micro zoned radiant (what type of radiant? how big is each radiant zone- radiation-wise?), it can short cycle on zone calls the boiler even with high-mass concrete or gypcrete radiant. But it becmes even more problematic when serving low-mass heat emitters such as baseboard.
A 105K-in modulating condensing boiler with a 5:1 turn down ratio can only throttle back to 21,000 BTU/hr-in, and at the ~120F average water temp needed to deliver 95% efficiency it can't drop below ~20,000 BTU/hr out. For a
typical fin-tube baseboard zone to deliver the 20KBTU/hr without cycling the boiler on/off it would need more than 90' of baseboard. If it only has half that much baseboard on the zone it will short cycle pretty badly on that zone, and less than that becomes a short-cycling boiler & efficiency killing nightmare.
Very few modulating condensing boilers have sufficient internal thermal mass to suppress short cycling, and the system may need a high-mass buffer tank or thermally massive hydraulic separator to fix it.