This forum is great! Thanks in advance for any help you can provide.
I'm currently in the planning stages for a theater/media room that will be extensively sound isolated and air sealed from the rest of the home.
The space has no windows, is all below grade in a basement and currently (unfinished) is a comfortable 72 degrees even in the hot humid summer months (90+degrees).
For sound isolation purposes the room will have r-13 and r-19 insulation in all wall and ceiling cavities and will be essentially air tight with acoustic caulk along all floor/ceiling/wall junctions as well as a completely air tight/sealed doorway.
According to my cooling load calculations, adults at rest produce ~500 BTU/hr and with a maximum occupancy of 9 seats, total body heat will approach (500btu *9=) 4500 BTU/hr. A video projector will also be located in the space which produces (655 watts * 3.41=) 2233 BTU/hr. Total cooling load of (2233btu+4500btu=) 6733 BTU/hr
Converted to CFM (400cfm=12,000btu/hr) my total cooling load requires 224cfm of cool air
All other equipment and heat sources will be located outside the space and managed/ventilated separately.
My question is about the type and number of minisplit units (low noise) that would be needed to ventilate the space which is 800sf in total area and ceiling height of 9ft, but has some irregularities in shape (open concept) that may prevent cool air from being dispersed evenly (pictured below with wall partitions in red)
My initial thought is to have a celling mounted MLZ model 9k btu Mitsubishi mini split cassette in the front of the main room (pictured in blue), but my concern is: will this circulate enough air to ventilate the adjacent spaces?
Should I size up to the 12k btu unit given the 8000 cubic feet of space to fill, or consider another 9k unit in the game room?
I'm currently in the planning stages for a theater/media room that will be extensively sound isolated and air sealed from the rest of the home.
The space has no windows, is all below grade in a basement and currently (unfinished) is a comfortable 72 degrees even in the hot humid summer months (90+degrees).
For sound isolation purposes the room will have r-13 and r-19 insulation in all wall and ceiling cavities and will be essentially air tight with acoustic caulk along all floor/ceiling/wall junctions as well as a completely air tight/sealed doorway.
According to my cooling load calculations, adults at rest produce ~500 BTU/hr and with a maximum occupancy of 9 seats, total body heat will approach (500btu *9=) 4500 BTU/hr. A video projector will also be located in the space which produces (655 watts * 3.41=) 2233 BTU/hr. Total cooling load of (2233btu+4500btu=) 6733 BTU/hr
Converted to CFM (400cfm=12,000btu/hr) my total cooling load requires 224cfm of cool air
All other equipment and heat sources will be located outside the space and managed/ventilated separately.
My question is about the type and number of minisplit units (low noise) that would be needed to ventilate the space which is 800sf in total area and ceiling height of 9ft, but has some irregularities in shape (open concept) that may prevent cool air from being dispersed evenly (pictured below with wall partitions in red)
My initial thought is to have a celling mounted MLZ model 9k btu Mitsubishi mini split cassette in the front of the main room (pictured in blue), but my concern is: will this circulate enough air to ventilate the adjacent spaces?
Should I size up to the 12k btu unit given the 8000 cubic feet of space to fill, or consider another 9k unit in the game room?