What I've read about hard starts is you have more available current to turn the compressor over from a dead stop, allegedly, over time, will burn the compressor windings out. Mine with the 5-2-1 hard start sure fires faster and easier "audibly", at my house.
I suspect you are mistake about the hard start system increasing the starting current from the mains.

I suspect that you read increased starting torque, and presumed higher current. As I read it, the hard start kit adds a capacitor into the circuit during starting to increase the phase shift and therefore the torque.

What I know is that 3-wire pump with a start capacitor is easier on a generator during starting (requires less V-As) than classic 2-wire pump.

My suspicions could be wrong. Can you find anybody who says the hard start kit causes an increase in starting amps?
 