How does this look?

Discussion in 'Shower & Bathtub Forum & Blog' started by amdskip, Mar 4, 2008.

  1. amdskip

    amdskip New Member

    Joined:
    Jan 30, 2008
    Location:
    Illinois
    Wanted to make sure this looked ok before I went sealing it up.

    Pictures

    There are a few pictures in there before that one if you use the arrows at the top to view them.

    Yes I am a messy plumber, practice makes perfect right:D
     
  2. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego, CA
    Houston, we have a problem!

    You should not use PEX, or CPVC, for the tube leading down to the tub spout. Because of the small ID, when you are running water to the tub, you may well have some water dribbling out of the SHOWER HEAD. Some brands mention this in the installation instructions, some don't, but expect trouble. You should either do that drop in copper, or bump it up to 3/4 CPVC.
     
    Last edited: Mar 6, 2008
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. amdskip

    amdskip New Member

    Joined:
    Jan 30, 2008
    Location:
    Illinois
    Thanks, I'll get some copper for that.

    My instructions are mostly pictures:(
     