How do you stop an airhandler from condensating

Users who are viewing this thread

droemer

New Member
Messages
10
Reaction score
0
Points
0
Location
Bradenton, Fl
Our new airhandler is condensating just like the old on ethat was replaced. The A/C company has increased the plenum; the supply was lengthened and angled to eliviate turblance on the blower, etc.

Does anyone have any ideas? It appears that the A/C company is just guessing.

Thanks,
Doug:confused:
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Our new airhandler is condensating just like the old on ethat was replaced. The A/C company has increased the plenum; the supply was lengthened and angled to eliviate turblance on the blower, etc.

Does anyone have any ideas? It appears that the A/C company is just guessing.

Thanks,
Doug:confused:

Where is the Air Handler located? Basement, Crawlspace, Attic?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Condensing HOW? Evaporator coils are intended to condense moisture out of the air. Are you saying you have condensation on the outside or on ducts or pipes?
 

droemer

New Member
Messages
10
Reaction score
0
Points
0
Location
Bradenton, Fl
The airhandler is located in the garage. The airhandler is suspended from the garage ceiling. It is condesating on the bottom and side; closest to the blower motor and supply plenum.
 

Bill Arden

Computer Programmer
Messages
584
Reaction score
0
Points
0
Location
MN, USA
Website
www.billarden.com
The airhandler is located in the garage. The airhandler is suspended from the garage ceiling. It is condesating on the bottom and side; closest to the blower motor and supply plenum.

It sounds like it's located in a moist area and is condensing just due to the return air.

Is there any way to make removable Styrofoam panels that enclose the unit?

Edit:
Can you take a surface temperature measurement and compare that to the outside dew point?
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Our new airhandler is condensating just like the old on ethat was replaced. The A/C company has increased the plenum; the supply was lengthened and angled to eliviate turblance on the blower, etc.

Does anyone have any ideas? It appears that the A/C company is just guessing.

Thanks,
Doug:confused:

Read my post titled, “Air handler / duct work problemâ€, and the post titled, “How much duct work fo I needâ€.
I brought up the same question about a pressure test, and after some research, I found some good information on how much pressure, should be in the return side of the air handler. I have made an improvement on the unit, and it is 100 % better then what it was! I made my own manometer for around $20.00, (with the help of this great, great forum).

Mike
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
condensation

IF a metal surface is chilled below the air's dew point, AND the air is humid, it WILL condense, period. It is a matter of physics. You have to raise the metal's temperature, which may not be possible if it cannot be internally insulated, (or you cannot raise the system's air temperature), or lower the humidity in the area, which may also be impossible, or separate the air from the metal with some sort of covering or insulation blanket.
 