A Navien tankless WH equipped with a built-in circulation pump will be an 'A' series model such as NPE-240A. The non 'A' models do not incorporate a pump.
Although an 'A' model has a pump, do not assume it is configured for recirculation through the home's plumbing.
1st, the dedicated return line would need to be actually connected to the Recirculation Water Supply port on the bottom of the WH. If that port remains capped, a return line is not connected.
2nd, if a return line is connected, there is a 2-way valve inside the WH that must be in the External position for the return line to be connected to the circulation pump inlet. If that 2-way valve remains in the Internal position, recirculation will not occur through the home's plumbing.
3rd, the WH's internal DIP switches must be set appropriately for external circulation.
Below are diagrams from the NPE-240A manual. You didn't specify the Navien model you obtained, so if it is another model, your manual may specify alternate settings.
Although an 'A' model has a pump, do not assume it is configured for recirculation through the home's plumbing.
1st, the dedicated return line would need to be actually connected to the Recirculation Water Supply port on the bottom of the WH. If that port remains capped, a return line is not connected.
2nd, if a return line is connected, there is a 2-way valve inside the WH that must be in the External position for the return line to be connected to the circulation pump inlet. If that 2-way valve remains in the Internal position, recirculation will not occur through the home's plumbing.
3rd, the WH's internal DIP switches must be set appropriately for external circulation.
Below are diagrams from the NPE-240A manual. You didn't specify the Navien model you obtained, so if it is another model, your manual may specify alternate settings.